Don't do much heating stuff, so after a bit of advice please.

Have Y Plan System in my place and just recently when the hot water comes on so does the central heating. Even though central heating is set to off (and hot water is on auto) ?

Just to try and prove things have completely disconnected the room stat and still the same ?

Would I be right in thinking that it could be a fault with the zone valve.... there is a little level under it which I have tried in every position and this makes no difference ?

Many Thanks,

Sy
 
When the system is on and calling for water only, check the position of the lever on the valve body. As it's a mid position valve it has 3 positions, water only, heating only & both together. The valve will either be marked H for heating W for water & M for mid position (both calling) or A for heating B for water & AB for mid position (both calling)


It sounds like the valve is stuck in mid position or there could be a problem with the heating coil in the cylinder.
 
faulty zone valve pal,push the lever over as far as you can, (you should feel a spring resisting) there is a little catch to hook it in to at that end,feel the pipe going to the tank it should get hotter. rads will go off,get new valve.
 
Thanks Chaps...

Valve is really old, cant see anything on it for positions think they've all worn off..... best get my plumber mate round then when back from his hols to a stick a new one in
 
Thanks Chaps...

Valve is really old, cant see anything on it for positions think they've all worn off..... best get my plumber mate round then when back from his hols to a stick a new one in
It's probably just the solenoid gone Sy, you can easily replace it yourself (unless your plumber is cheap/free).

Try reaching around the back of the solenoid housing that's sitting on top of the valve (and feeling for the lever, only the tip of the lever normally protrudes through the housing (about half a centimetre or so)), the lever is often hidden coz of the orientation of the housing.
 

Reply to Bit of help please.... Y Plan in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

Unfortunately I don't think you will get an "off the shelf" diagram for the system you are trying to do The Wiser system is very adaptable but it...
Replies
1
Views
292
D
  • Article
W-plan pump run on Son recently moved into a 20 year old house with what appears to be a W-plan system using, I think a Worcester Bosch Greenstar...
Replies
0
Views
148
davidwf
D
I was thinking that when the new two port opens and turns boiler and pump on, the normally open port (priority) on the three port is uncontrolled.
Replies
12
Views
2K
Does this help, note com is out not in I have a extended version using this basic system.
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks