sparks monkey

Hi people

Maybe somone can give me some pointers, Generally with faults i'm pretty good but this one has got me stumped!
I was working in an old house that the owner required some modernising, so we did a kitchen and moved and added few lights and switches around as you do. The board was an old 16th wylex type with enough ways to slip in a new rcd unit. I tested the non rcd side and found a short live to earth 57M/ohms (the MCB was holding in), so i went to the van and swaped testers and tried my back up set, same result. I tracked it down to a radial lighting circuit serving 2 downstairs rooms and the upstairs. So i set about looking into checking the customer fitted fancy light fitting, not pretty and amongst the faults in them none of which were down L-E, i ended up at the end of the radial (typically) to the GU10 down lights we fitted. I then disconected the main feed to them, tested and the fault was there, i then disconnected the junction box and tested each cable and found the fault was on the downlighters side, i then disconected the middle downlight tested, the fault was on the both lives and both earths!!, so i disconnected all downlights, tested all cables and the fault had mysterously vanished! I checked all cable entries from factory connections to the main bodies for chaffing, everything was sound, I checked all the cable clamps for signs of a pressure fault, again nothing apparent, so i connected everything back up and its back!! I tested the earth for power and was getting about 0.02A (on an uncaliberated amp meter), MCB stays in everything works fine but its not right,

any ideas?
 
fixed it, crushed cable behind a joist, nuetral to CPC, back feeding through the lamps in the downlights, resulting in a L-CPC fault, text book stuff i suppose should have fouind it earlier, thanks for all your help
 
HI Spanks Monkey!.... quote 'Generally with faults i'm pretty good but this one has got me stumped!'

57million ohms ....erm! Someone is contradicting themselves!!!

PS yes i know I spelt your name wrong or did I .... maybe more study and less of that may stop you getting basics wrong!
 
Last edited by a moderator:

Reply to bizzare Line to CPC fault on lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
277
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
269
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
350

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
652
  • Question
At this "first" fitting it's loop in. The rest appear to be joint boxes and old par 38 light fittings. It is reasonably old wiring but not...
Replies
3
Views
335

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top