theoretical question:

if the main fuse is a 80A BS88 type IIb, tails are 25mm with 16mm earth, can i install a 10 way dual rcd board with a 100A main switch?

how is the total load calculated? all the MCB'sin your average 10 way bpard add up to way over 100A?
 
about right. 0.4. and @ exarmy. remember your 100A rating of your main sw. is just the max. current it can safely take. nbot as if it's an overload device.
 
BS 88 type IIB??
All domestic boards come with 100 amp main switch, not sure what your problem is!
Most, if not all domestic installations have breakers that add up to more than 100 amps. Common sense says that if you are not altering the installation to include extra loads then the main fuse will continue to be sufficient.
 
@ Jay Sparks

What goes beep, beep beep, beep?

Man utd open top bus going back into the garage.

Sorry mate couldn't resist and I'm not a footy fan. Oh well every rose as a thorn, you might do better next season. You've got to live and let die in that game I'm afraid.
 
@ Jay Sparks

What goes beep, beep beep, beep?

Man utd open top bus going back into the garage.


Sorry mate couldn't resist and I'm not a footy fan. Oh well every rose as a thorn, you might do better next season. You've got to live and let die in that game I'm afraid.


Bang Bang you shot me down, Bang Bang I hit the ground........
Harsh but fair.
I suppose in the end, "Every loser wins"

Jay
 

Reply to board change questions in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
483
What makes it a lack of space? I’d say to the customer to dismantle a cupboard or whatever to creat the space you need for the extra equipment...
Replies
1
Views
212