Called to a boiler fault today where the heating was not working - tenant just moved into house.
So I had a look and realised tat someone (probably the heating engineer who was there before me) had been altering the wiring. They had swapped connections about in the time click and room stat in the hope they would fix the problem
So I belled all the cables out and reconnected correctly through the time click and room stat, powered up and heating kicked on. Seemed to be good but when trying to switch the heating off it was staying on.
Double checked my wiring, all ok, but I was getting 230v back from the boiler to the switch wire of the room stat. I opened up the control panel of the boiler and noticed that the voltage was coming from the volt free contacts which read 'do not put voltage onto these terminals as this will result in severe damage to boiler'
I had wired the controls correctly, volt free, but is it possible that whoever was tampering with the wiring has put voltage onto these contacts and damaged the circuit boards, resulting in voltage back feeding from boiler to these terminals?
So I had a look and realised tat someone (probably the heating engineer who was there before me) had been altering the wiring. They had swapped connections about in the time click and room stat in the hope they would fix the problem
So I belled all the cables out and reconnected correctly through the time click and room stat, powered up and heating kicked on. Seemed to be good but when trying to switch the heating off it was staying on.
Double checked my wiring, all ok, but I was getting 230v back from the boiler to the switch wire of the room stat. I opened up the control panel of the boiler and noticed that the voltage was coming from the volt free contacts which read 'do not put voltage onto these terminals as this will result in severe damage to boiler'
I had wired the controls correctly, volt free, but is it possible that whoever was tampering with the wiring has put voltage onto these contacts and damaged the circuit boards, resulting in voltage back feeding from boiler to these terminals?