Many commercial boilers dont take kindly to suddenly have their power disrupted. Many boilers like to keep the pump running to dissipate heat to stop any damage to the boiler itself.

I agree with views here, what are we trying to achieve?

The last thing you need is an E-stop which stops the boiler firing, then as soon as you release the E-stop, the boiler fires up again, this is not an e-stop, this is a simple management of "Call for Heat"

A proper commercial E-stop for a gas appliance, for example would be connected to the gas supply, this would shut off the gas and the only way to reset would be a manual reset system, rather than just releasing the E-stop

Hope this helps

P&S
 
A proper commercial E-stop for a gas appliance, for example would be connected to the gas supply, this would shut off the gas and the only way to reset would be a manual reset system, rather than just releasing the E-stop

Hope this helps

P&S
BS6173 systems as an example, although I'm sure I've seen models that eset with just the single twist of the e-stop, once activated that is.
 
I have a boiler with a 20amp disconnect switch. The owner wants to add 2 mushroom head E-stops. If there is no e-stop terminals in the boilers control panel whats the best way going about this?
That’s simple just purchase 2 E-STOP buttons and buy 2 sets of NC contacts and wire your power feeding the boiler through the e-stops and then to the boiler. All you stated was it was 20 amps so we don’t know if it’s 120vac or 240vac but if you have a neutral you have to break it also. I’m assuming you have no low voltage controls so make sure the contacts are rated for 20 amps. You also could use a e-stop relay which would really be better but the wiring would be different
 
That’s simple just purchase 2 E-STOP buttons and buy 2 sets of NC contacts and wire your power feeding the boiler through the e-stops and then to the boiler. All you stated was it was 20 amps so we don’t know if it’s 120vac or 240vac but if you have a neutral you have to break it also. I’m assuming you have no low voltage controls so make sure the contacts are rated for 20 amps. You also could use a e-stop relay which would really be better but the wiring would be different
Appreciate your advice
 
I think the problem here is terminology, I suspect what your client wants is 2 latching stops, there is a habit to call these E-Stops regardless but it is the circuit that protects it that denotes whether it is or not even if it is inscribed, having said that modern units that comply to E-Stops are defined by colour distinction and sometimes complemented by symbols.
A red actuator against yellow is classed as a E-Stop designation (UK/EU), if I were you after clarifying with the customer I would get a latching stop button that does not meet that colour distinction therefore will not be acknowledge as an E-Stop.
If a genuine E-Stop system is required then it is likely the boiler will not have the correct circuitry to do this, you would have to design and install yourself as a separate system that gives failsafe functionality and interrupts the boilers controls at 2 or more points allowing normal rundown procedures so as not to stop any overrun features of the boiler like fans or pumps that need to ensure safe shutdown.

I will reiterate, we need to understand what the customer is asking and why, what is the full reason for this to be implemented, if there exist no hazards to be averted and it is simply for convenience then latching 'functional stops' are a simple cheap and prefered option that just break the call signal.

@Megawatt - we must be careful on terminology here, you cannot call them E-Stops if they are not serving that purpose as well as having the correct control system to meet those standards, putting latching stops or even push stops that are colour coded to meet E-Stop classification does not make them E-Stops unless the system they are applied to meets the standards, they are functional stops otherwise.. I get this alot in my job where a customer will ask for extra E-Stops on the machine and they are told there machine has no E-Stop system to do that, they make the mistake of assuming the actuator design is what an E-Stop is and that is wrong, the control circuit is what makes that classification... Yes through out the industry we all call these points E-Stops regardless, they are advertised as such and sold as such but to be absolutely correct on this and the fact we are talking safety of a system we thus cannot be loose with terminology in this thread, we need to understand the reasoning on the customer and what hazards if any is trying to be averted.
 
Last edited by a moderator:
I think the problem here is terminology, I suspect what your client wants is 2 latching stops, there is a habit to call these E-Stops regardless but it is the circuit that protects it that denotes whether it is or not even if it is inscribed, having said that modern units that comply to E-Stops are defined by colour distinction and sometimes complemented by symbols.
A red actuator against yellow is classed as a E-Stop designation (UK/EU), if I were you after clarifying with the customer I would get a latching stop button that does not meet that colour distinction therefore will not be acknowledge as an E-Stop.
If a genuine E-Stop system is required then it is likely the boiler will not have the correct circuitry to do this, you would have to design and install yourself as a separate system that gives failsafe functionality and interrupts the boilers controls at 2 or more points allowing normal rundown procedures so as not to stop any overrun features of the boiler like fans or pumps that need to ensure safe shutdown.

I will reiterate, we need to understand what the customer is asking and why, what is the full reason for this to be implemented, if there exist no hazards to be averted and it is simply for convenience then latching 'functional stops' are a simple cheap and prefered option that just break the call signal.
Why they are doing this makes no sense. It's a boiler for in floor heat. Incase of an emergency or situation they want to be able to kill power with mushroom head e-stop. At another location we just had 2 single pole switches as "e-stops"
 
Why they are doing this makes no sense. It's a boiler for in floor heat. Incase of an emergency or situation they want to be able to kill power with mushroom head e-stop. At another location we just had 2 single pole switches as "e-stops"
This is why you need to have a long in depth discussion with the client, it may be the case it is a zone they want to close off and not the entire system, it may not be a hazard but simple convenience which does not warrant any kind of E-Stop system.
 
This is why you need to have a long in depth discussion with the client, it may be the case it is a zone they want to close off and not the entire system, it may not be a hazard but simple convenience which does not warrant any kind of E-Stop system.
Email I received says "e-stops interlocking with boiler". Ill have a chat with them. If I use single pole switches instead of e-stops I'm sure they will be ok with that
 
Email I received says "e-stops interlocking with boiler". Ill have a chat with them. If I use single pole switches instead of e-stops I'm sure they will be ok with that
The lack of info from your client means you are guessing here, they have requested E-Stops, your job is to query they understand the difference here, if it is a E-Stop system they really do need then the design, implementation and liability for it will lie permanently on your shoulders.
If you can establish like I expressed in my recent post that there is simply confusion here based on terminology then it may be a simple job as you suggest but I wouldn't want to be in your shoes if you make a fundamental mistake at this stage and in the near future someone is hurt or property damage occurs.

I hope this all is just a mixup that is causing confusion, I fit E-Stop systems for a living and one of the first things you do is establish what is been requested and how it would be implemented, this is all done at the risk assessment stage. I would also like to mention that if this is indeed a genuine E-Stop system you are installing then are you insured to do this work, my insurance for machinery control and upgrade (which essentially this is if you are installing a E-Stop circuit to a commercial boiler) means my insurance is about 5X higher than a standard installation Electricians, you may need to consult with your insurance company to see if you are covered here, the amount of people I see with basic cover and playing about with machines is gobsmacking in my industry as they never consider they are not covered for the work when asked.
 
The lack of info from your client means you are guessing here, they have requested E-Stops, your job is to query they understand the difference here, if it is a E-Stop system they really do need then the design, implementation and liability for it will lie permanently on your shoulders.
If you can establish like I expressed in my recent post that there is simply confusion here based on terminology then it may be a simple job as you suggest but I wouldn't want to be in your shoes if you make a fundamental mistake at this stage and in the near future someone is hurt or property damage occurs.

I hope this all is just a mixup that is causing confusion, I fit E-Stop systems for a living and one of the first things you do is establish what is been requested and how it would be implemented, this is all done at the risk assessment stage. I would also like to mention that if this is indeed a genuine E-Stop system you are installing then are you insured to do this work, my insurance for machinery control and upgrade (which essentially this is if you are installing a E-Stop circuit to a commercial boiler) means my insurance is about 5X higher than a standard installation Electricians, you may need to consult with your insurance company to see if you are covered here, the amount of people I see with basic cover and playing about with machines is gobsmacking in my industry as they never consider they are not covered for the work when asked.
I really appreciate you're advice, friday I asked for more information based off our discussion and they emailed me what I said above. "E-stops to interlock with boiler for emergency shutdown "
 
I really appreciate you're advice, friday I asked for more information based off our discussion and they emailed me what I said above. "E-stops to interlock with boiler for emergency shutdown "
That reply for me does not tell me the client understands the difference between E-Stop and Functional Stop, there is no mention of reasoning here to maybe give us a better idea and like what was mentioned by another member, most boilers will have a shutdown sequence, is that clearly understood by your client, pump circulation, venting fans etc may continue for a preset period IE a controlled shutdown.
I guess you have emailed the client to get that response but if you fail to give all the information and ask the right questions you will get ambiguous answers as such, from that reply I am still no clearer as to what your customer is asking for, the cost difference here could be shy of 1K if we are indeed fitting and integrating a compliant E-Stop system but the category of the system needed will have to be determined by risk assessment and the outcome may simply warrant a small adaption of the boiler controls all the way to an independent safety control board that meets a higher category system.

What confuses me here is what perceived hazards warrant a Emergency Stop system on a standard commercial boiler for heating that it doesn't already have implemented itself, this is why I think your customer may be at crossed purposes and mixing up terminology here.
 
The requirement for an e-stop on the system is down to the integrator, by LAW.
The boiler installation must have been CE marked as an assembly to comply with the LAW.
Forget BS 7671 totally irrelevant.
You are now into EN 60204-1, ISO 13850, ISO 13849-1 & ISO 13849-2.
Then the C-Type standards for boilers.
An emergency stop does not HAVE to shut everything down immediately.
It is written into the LAW and standards such that it can shut things down as quickly as possible in a safe manner.
Examples are cited of exothermic process reactions which may take hours to stop completely in response to an e-etop safety function command.
Other things may have fastest possible deceleration to a standstill under power, with power remaining on to the actuators.
The other thing that MUST be considered is that an e-stop function has a limited life before the components must be changed in accordance with the harmonised standards.
This is taken as a 20 year life, and if the e-stop is going to be used to shut the equipment down at the end of a day then that is 365x20 = 7300 operations in 20 years, the ISO 13849-2 validation needs to reflect that.
This is a minefield that could end up badly if the correct procedures are not followed.
For your own benefit make sure that you are insured to work on boiler controls, and under EN 60204-1 as in the Machinery Directive (UK Supply of Machinery Safety Regulations) and to design and implement safety functions.
You are stepping into an area that most electrical contractors policies do not cover you for.
You could easily end up in prison or bankrupt if things went wrong.
 
That reply for me does not tell me the client understands the difference between E-Stop and Functional Stop, there is no mention of reasoning here to maybe give us a better idea and like what was mentioned by another member, most boilers will have a shutdown sequence, is that clearly understood by your client, pump circulation, venting fans etc may continue for a preset period IE a controlled shutdown.
I guess you have emailed the client to get that response but if you fail to give all the information and ask the right questions you will get ambiguous answers as such, from that reply I am still no clearer as to what your customer is asking for, the cost difference here could be shy of 1K if we are indeed fitting and integrating a compliant E-Stop system but the category of the system needed will have to be determined by risk assessment and the outcome may simply warrant a small adaption of the boiler controls all the way to an independent safety control board that meets a higher category system.

What confuses me here is what perceived hazards warrant a Emergency Stop system on a standard commercial boiler for heating that it doesn't already have implemented itself, this is why I think your customer may be at crossed purposes and mixing up terminology here.
Hahahaha im right there with you on that, it isn't needed.
 
The requirement for an e-stop on the system is down to the integrator, by LAW.
The boiler installation must have been CE marked as an assembly to comply with the LAW.
Forget BS 7671 totally irrelevant.
You are now into EN 60204-1, ISO 13850, ISO 13849-1 & ISO 13849-2.
Then the C-Type standards for boilers.
An emergency stop does not HAVE to shut everything down immediately.
It is written into the LAW and standards such that it can shut things down as quickly as possible in a safe manner.
Examples are cited of exothermic process reactions which may take hours to stop completely in response to an e-etop safety function command.
Other things may have fastest possible deceleration to a standstill under power, with power remaining on to the actuators.
The other thing that MUST be considered is that an e-stop function has a limited life before the components must be changed in accordance with the harmonised standards.
This is taken as a 20 year life, and if the e-stop is going to be used to shut the equipment down at the end of a day then that is 365x20 = 7300 operations in 20 years, the ISO 13849-2 validation needs to reflect that.
This is a minefield that could end up badly if the correct procedures are not followed.
For your own benefit make sure that you are insured to work on boiler controls, and under EN 60204-1 as in the Machinery Directive (UK Supply of Machinery Safety Regulations) and to design and implement safety functions.
You are stepping into an area that most electrical contractors policies do not cover you for.
You could easily end up in prison or bankrupt if things went wrong.

I re-iterate the OP is in the USA.
CE markings and BS, EN, standards therefore don't mean a thing.
 
Boilers no matter country you are in need to be shut down correctly according to the MI's.

I suggest OP forwards the email request from client to the boiler tech support team and ask them how best to "shut down in case of emergency" - AKA, lazy mans way of turning off at night, lol
 

Reply to Boiler emergency e-stop in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Outside socket… ok. But you say the fcu for boiler is beside the outside socket… is the boiler outside too? FCU’s have an IN and an OUT… the OUT...
Replies
2
Views
157
T
  • Article
Indirect (Boiler Fed) Megaflo Doesn't Stop Heating Hi, I noticed yesterday that when my HW is on, that the boiler runs constantly... I even...
Replies
0
Views
236
techweb
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top