L

Leepato

I looked at a job today and noticed the boiler in a small bathroom was plugged into a socket that had been put in an an extra by the look of it. I know that a socket is allowed in the bathroom but has to be 3mts away from zone 1. This room isn't 3mts big though. Is replacing the socket to a switched fuse spur acceptable? Or what should be done?

Cheers
 
Looking at the on site guide if it 0.6mts away from the shower it shows it being outside of zone 2. A switched spur should be adequate then as the boiler will be permanently connected and in an area that will avoid any water jets. Am I right in thinking this?

The circuit is not protected by an rcd .
 
if you fit a FCU, you will need to add RCD and check earthing and bonding, replace if needed,and notify LABC. cost will most likely make the customer say b******s, and you'll need to walk away.
 

Reply to Boiler fitted in bathroom query in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
746
Yes, that was actually something making me uncomfortable too, the bonding of it all. I need to have another look at it, I'm not sure if the...
Replies
2
Views
804

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top