Boiler room sockets - do they require an RCD? | on ElectriciansForums

Discuss Boiler room sockets - do they require an RCD? in the Australia area at ElectriciansForums.net

Joined
Jun 18, 2008
Messages
366
Reaction score
8
Hi all

A customer has had a recent PIR at a commercial premises and some boiler room sockets have been flagged as a D1 for not having RCD protection. All are in the locked room which is only accessible to the caretaker. I don't see a problem with this and don't see why they need an RCD adding. Only one can be used for outside equipment, which is an RCD socket. The guy that did the PIR said it's because it's a boiler room but that's not a special location or anything. What are your thoughts?
 
It appears the sockets are intended for use by a skilled or instructed person, the one used to supply equipment outdoors has RCD protection, should be no Code at all, as it all complies.

This was exactly my thinking, no one has access to the room and besides all cables are in galv conduit too. The chances of any of the sockets getting wet are nil, none are anywhere near the boilers. Thanks for the comments all, I've been given the job already but I'm sure they'll appreciate the honesty of telling them it doesn't need anything doing! He doesn't need half the sockets anyway so I'll be blanking some off for him so can still give them a cert covering it so they know the circuit's ok.

Cheers again :)
 

Reply to Boiler room sockets - do they require an RCD? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

Similar threads

Stick the socket in a large plastic wall box with hinge and padlock. Give customer letter with key...
2
Replies
17
Views
4K
As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top