New shaver socket outside zone in bathroom. (FCU outside the room,17th ed'n board).
Checking the bathroom to see if any supplementary bonding needed, turned out the sink and bath taps were hovering at about 5K Ohm (ie >1667 and < 22K).
Turns out the owner had interrupted the hot and cold Cu pipes with single push-fittings in the loft, and that was the source. (Main equipotential bonding was very effective before then, rest of the house all in Cu). So Supplementary bonding required in bathroom, but this would have been VERY disruptive, and customer wouldn't take it on.
Easy however to bond across the two plastic joints in the attic with 10mm strap and clamps. Nice and neat, very effective and safely out of the way. Bathroom taps are no longer Extraneous, at a small fraction of an ohm.
So technically I don't see this as any different to what I might have found had the plastic parts not been there, and (just say) a compression joint had provided a low enough resistance. I'd have measured it, then been none the wiser and equally wouldn't have fitted any Supplementary bonding.
Where do I sit with this re 701.415.2? Part Vi just says "effectively connected", which it is. - but it's not supplementary bonding.
Chasing walls/tiles off etc to get the cable in wasn't going to happen.
Might I record this as a departure, and get on with things?
Checking the bathroom to see if any supplementary bonding needed, turned out the sink and bath taps were hovering at about 5K Ohm (ie >1667 and < 22K).
Turns out the owner had interrupted the hot and cold Cu pipes with single push-fittings in the loft, and that was the source. (Main equipotential bonding was very effective before then, rest of the house all in Cu). So Supplementary bonding required in bathroom, but this would have been VERY disruptive, and customer wouldn't take it on.
Easy however to bond across the two plastic joints in the attic with 10mm strap and clamps. Nice and neat, very effective and safely out of the way. Bathroom taps are no longer Extraneous, at a small fraction of an ohm.
So technically I don't see this as any different to what I might have found had the plastic parts not been there, and (just say) a compression joint had provided a low enough resistance. I'd have measured it, then been none the wiser and equally wouldn't have fitted any Supplementary bonding.
Where do I sit with this re 701.415.2? Part Vi just says "effectively connected", which it is. - but it's not supplementary bonding.
Chasing walls/tiles off etc to get the cable in wasn't going to happen.
Might I record this as a departure, and get on with things?