Bonding again | on ElectriciansForums

Discuss Bonding again in the Australia area at ElectriciansForums.net

P

Plonker 3

Went to look at a job the other day where the water and gas were correctly bonded in the house. But they also had a outhouse which was connected to the house via a covered walkway.

Inside there was a 2 way RCD board fedding a light and several sockets in the outhouse.

There was also a incoming water pipe from the house which came from under the floor. Would this also need bonding too or because it is bonded on the house is that satisfactory?
 
That is a good one and here we go.

If you've extended the equipotential zone to the outhouse and that is bonded, and you take a water feed to the outhouse from the bonded equipotential zone, then theoretically there should not be any PD, and as a outhose in the BS 7671 is not classed as a special location when regarding bonding, then I would say no need to bond, especially as you have RCD protection.

But as Tel says there are several imponderables, and the main one for me would be continuity of that water pipe with the bonding.
 
Last edited:
I did carry out a quick contiuity test between the earth bar in the RCD board and the water pipe and it was 0.63 ohms.

I was only carrying out a replacement of a batten lamp holder so I don't have to bond it for that do I? I told the customer I would write up a quick report for her to inform her of my findings and told her that should any installation work be carried out in the out house it would need bonding then.
 
Personally I would have done a continuity test from pipe to MET and then an IR from pipe to MET just to see what I had.

Again because of the RCD protection I would not worry about just the changing of a batten holder. I would though have tested the RCD with all 7 tests, I assume it is a 30mA kind

Finally before you put things in writing to a customer make sure what your writing is correct. Don't go advising them that if future work is carried out, you HAVE to bond that pipe, when you may not have to. Bonding something that does not need bonding, is just as dangerous as not bonding something that does
 
Again because of the RCD protection I would not worry about just the changing of a batten holder. I would though have tested the RCD with all 7 tests, I assume it is a 30mA kind
Yes it was 30ma and I carried out the relevant tests and filled out the results on a MWC.

Finally before you put things in writing to a customer make sure what your writing is correct. Don't go advising them that if future work is carried out, you HAVE to bond that pipe, when you may not have to. Bonding something that does not need bonding, is just as dangerous as not bonding something that does

I know that, was just looking for some clarity on the situation, so I should say it would need testing to the current BS7671 standards at the time, and may need bonding if it doesn't meet these standards, don't really want to confuse the customer too much or try and frighten them into thinking their house is unsafe.

Does anyone have a PDF of a leaflet I could give to the customer explaining bonding?
 
Take the scenario on, you have water service coming into the house that is bonded as per the 17th. The house is all copper and there is an outside tap fed from a spur from the kitchen sink.

Now because you have bonded the services coming into the house the whole house in now an equipotential zone with no potential difference.

Next to the tap say 4ft away you have a socket again spurred from the kitchen RFC, so your pipe and socket are extensions from the equipotential and therefore bonded and are of the same potential .................but your now in the garden and of course that is of a different potential and so what is the best solution
 
Take the scenario on, you have water service coming into the house that is bonded as per the 17th. The house is all copper and there is an outside tap fed from a spur from the kitchen sink.

Now because you have bonded the services coming into the house the whole house in now an equipotential zone with no potential difference.

Next to the tap say 4ft away you have a socket again spurred from the kitchen RFC, so your pipe and socket are extensions from the equipotential and therefore bonded and are of the same potential .................but your now in the garden and of course that is of a different potential and so what is the best solution

If you are in the garden you are completely surrounded by earth potentials,you cant create an equipotential zone,no point in bonding anything.
 
Right, so it should be bonded in the future, due to it being buried underground and introducing a different potential to the outhouse?

Then there is a chance because of it being buried and you've extended your equipotential zone from the house into the outhouse then yes it would most likely be at a different potential and need bonding, but you would need to bring it back into the equipotentiall zone by bonding back at MET.

What I was thinking on your OP was a pipe not buried but say run around a wall. I know you said under the floor, but until actually said buried.
 

Reply to Bonding again in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
831

Similar threads

  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K
The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...
Replies
3
Views
604

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top