Doing a bathroom redo next week and suspect no earth bonding. If I used plastic pushfit tap connectors would that mean I don't have to earth bond the pipework in the bathroom.??:confused:
 
the pipe work should be bonded is if it higher than 1670 ohms with a long lead from the main earth as long as all circuits are rcd protected. If you are using plastic fitting the pipe may not be with in that reading. so its as scott says depends on the rest of the pipe work in the room
 
Leekemp have another read at your testing. OP didnt state in any RCD on circuit. He also didnt state tyope of overcurrent devgice used. Remember your 50v rule!!!!


Long lead test all metalic parts from your MET in the "Special location" Kitchens are included in part p If the reading is OVER 0.05 ohms then start putting in Suplimentery bonding
 
Sorry Scott I will keep quite from now on.
I was only quoting from the bloke that I did my 17th edition course with.
There is no need to go over the top (red underlined) I made a mistake its not a big deal.
 
hi

if every circuit in the bathrom is rcd protected then supp bonding is no longer required and if carrying out any new work it needs to comply with 17th and needs to be rcd protected, so if you have any circuits you havnt worked on that are not rcd protected you will need to introduce supp bonding... thats how i understood it to be anyway. correct me if i am wrong.

cheers
 
Leekemp i did underline it for a reason you quoted a number of the book without all the details doing this can be dangerous. If in this case it was an old d.b or even a 16th edition split board and the shower being over 32A wasnt on an rcd a resistance fro 0.05 to 1667ohms on the bonding in the event of a fault could be LETHAL.
The 17th course will only tell you how to find information in th book and the new layout. Go for a 2391-01 course that teaches you how to use the book and understand it.

remember a little knowlege can be a dangerous thing!!
 
Thanks for the reply guys...AS you can tell not an experianced electricain, but with your help I will learn a bit more.:eek:
The long lead test does that have to be done with a wander lead? or will similar size cable do and just calabrate the tester to zero.?
 

Reply to Bonding and plastic tap connectors in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
I
  • Article
Water hammer/noise from pipework at night? I attended a Job where the customers complained about noisy pipes more often late at night bur...
Replies
0
Views
195
Illuminate
I

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top