Joined
Oct 2, 2012
Messages
41
Reaction score
8
Location
Midlands
Im doing some alterations in part of a school. I noticed a water stop cock that has no bonding conductor. Its not the main stop cock as that is another part of the school. I carried out an R2 from the local sub board i am working from and got 0.32.
Am required to bond it to bring it within the 0.05 requirement or is it ok with the main bond at the main stop cock? I would just do it but its a bit of a job so if its not required then i will leave it...
Cheers
 
0.05 requirement

There is no requirement for a main protective bonding conductor to have a resistance not exceeding 0.05 Ohms. A low resistance (e.g. not exceeding 0.05 Ohms) is between the clamp and what it is connected to in order to ensure that there is an adequate connection.
 
thanks for pointing that out. so many guys erroneously have this silly figure of 0.05ohms as the max. resistance of a bonding conductor.
 
thanks for pointing that out. so many guys erroneously have this silly figure of 0.05ohms as the max. resistance of a bonding conductor.

Indeed. Would be curious as to which Reg. they believe requires it! Only mentioned in GN3 (in the context mentioned above) as far as I am aware.
 
sadly a case of reading things wrong. for a long time, many sparks thought it was not done to extend pme to a garage/shed and so spent hours banging in useless short thin rods.
 
estimate the length of the bonding conductor. look up the resistance/m for the csa then you can guesstimate what it should be.

just wondering what mary whitehouse has to do with it ( she wanted to stop cock)
 
I was always taught that to guesstimate what the resistance should be on a bonding conductor is 0.05 ohms per meter so on a reading of 0.32ohms your run should be roughly 6.5m.

However like said said previous I think you should check if this could bring an earth potential otherwise you should be fine.
 

Reply to Bonding conductor in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
391
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
975
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
669
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top