Being unsure of an answer myself I searched for something simillar
Here is a quote from someone on the Iet forum that may be of interest to you
Whilst the primary function of the metallic armouring of an armoured cable is to provide overall strength, it may be used as a circuit protective conductor (cpc), main protective bonding conductor or, where practicable, an earthing conductor.
Whichever of these three functions is to be performed by the armouring of a cable, all the relevant requirements of BS 7671 need to be satisfied. The armouring of a cable may be used for more than one of the functions if all the appropriate requirements for each function concerned are met.
Like any conductor used as a cpc, armouring will experience thermal stress (heating effects) if it is subjected to earth fault current. To withstand this stress safely, the cross-sectional area (csa) of armouring used as a cpc must be not less than that determined by one of the two methods referred to in Regulation 543.1.1 of BS 7671, namely calculation or selection.
In an installation where Protective Multiple Earthing (PME) conditions apply (that is, where the means of earthing for the installation is a PME earthing facility), main protective bonding conductors have to carry sustained currents under certain conditions, which may result in heating of the bonding conductors. The armouring of a cable should not be used as a main protective bonding conductor where PME conditions apply.