Robo

TNCS supply.

Iv been asked to do an eicr.The garage is connect to house using 6mm 3c swa. There a plastic waterpipe which enters the garage. then goes to a sink and toilet which has some exposed copper sections on show. Do they need bonding? Both house and garage have rcd protection
 
IR test between the melal pipework and your earth terminal. if rfeading is > 22k ohms, not extraneous so no need to bond.
 
The question is the service extraneous......unlikely if plastic. The exposed copper sections are also unlikely to be extraneous unless they are in contact with the ground or structural steel. If the garage is steel framed that may require main bonding. It is possible to test for ECP's. IR test between suspected ECP's and the MET. Less than 22Kohms is assumed ECP and needs bonding.
One point is that you state 6.0mm SWA.....this will not be suitable as a main bond to ECP's if the supply is TNCS....a minimum 10.0mm copper will be required back to the MET at the intake.

Edit...tel types quicker lol.
 
So if i IR test between earth terminal in garage and ECP (sections of exposed copper pipe near sink) the reading needs to be above 22 kiloohms 22000 ohms and i dont need to bond. But if its below that i will need to put a 10mm earth in from the MET at the house.?

Will this method apply with regards to the copper bath to.

thanks
 
So if i IR test between earth terminal in garage and ECP (sections of exposed copper pipe near sink) the reading needs to be above 22 kiloohms 22000 ohms and i dont need to bond. But if its below that i will need to put a 10mm earth in from the MET at the house.?

Will this method apply with regards to the copper bath to.

thanks

That earth terminal in the garage is your Earth Marshaling Point (EMP) your MET is most likely at the origin of the installation in the house. You need to test there
 

Reply to bonding in detached garage in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
332
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
859
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
983

Similar threads

My wife’s Evoque gets about 32 miles on a full charge and I get about 28 miles on my F-Pace. I don’t know how long a full charge takes but I...
Replies
13
Views
1K
I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
510

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top