Just remove the main earthing conductor from the MET as if you were measuring Ze and test between that (the earth) and the pipe. No parallell paths then.
 
Of course not, but SBSB said if the incomer is plastic then the PLUMBING isn't an extraneous conductive part. I would test the metal pipework nearest to the connection to the plastic incomer and if extraneous; bond.

Sorry mate that wasn't directed at you lol
 
Just remove the main earthing conductor from the MET as if you were measuring Ze and test between that (the earth) and the pipe. No parallell paths then.

Yes there are. You are likely to get parallel paths from other extraneous services such as gas/oil which are mechanically connected to the same system as the water via boilers etc and not practical to remove.Disconnecting main earths and bonds still does not eliminate misleading readings.
 
Last edited by a moderator:
That's assuming other services have been bonded, which if they have and it is affecting the water then bonding it anyway isn't going to do any harm. If the bonds are affecting the water so much that you get a 0.05 - 0.06 reading then some would argue that it would be safe to assume a bond is already in place and to leave it and crack on.
 
A local firm in my area have just had the nic crawling all over them because they didn't run a main bond to the water main. Incoming pipe was plastic covered copper, rest of houses in plastic (scheme).
I would still run a bond and connect it on to the stop valve, this would satisfy the sheets, regs, and any electrician who looks at it.
 
If told to do it by the foreman do it and when questioned say that Mo Fo told me to do it!

Do you do everything a foreman tells you to do??? :)
 
That's assuming other services have been bonded, which if they have and it is affecting the water then bonding it anyway isn't going to do any harm. If the bonds are affecting the water so much that you get a 0.05 - 0.06 reading then some would argue that it would be safe to assume a bond is already in place and to leave it and crack on.

You miss the point mate,existing bonding has nothing to do with it. If a gas pipe (for example) is extraneous,it will be at earth potential or thereabouts whether it is bonded or not.There is likely to be some electrical continuity to the water system via mechanical connection between pipework at a boiler even with all bonds/earth disconnected. Thats why the IR test to establish whether bonding is required is nearly always misleading.....(IMO!)
 
You miss the point mate,existing bonding has nothing to do with it. If a gas pipe (for example) is extraneous,it will be at earth potential or thereabouts whether it is bonded or not.There is likely to be some electrical continuity to the water system via mechanical connection between pipework at a boiler even with all bonds/earth disconnected. Thats why the IR test to establish whether bonding is required is nearly always misleading.....(IMO!)

No, I'm not missing the point, instead I am agreeing lol.

Misleading readings possible but no harm done if bonded anyway :)
 
A local firm in my area have just had the nic crawling all over them because they didn't run a main bond to the water main. Incoming pipe was plastic covered copper, rest of houses in plastic (scheme).
I would still run a bond and connect it on to the stop valve, this would satisfy the sheets, regs, and any electrician who looks at it.

If the incomer is copper it's almost certainly extraneous and needs bonding regardless of the rest of the install being plastic.
 
The more I read these threads regarding bonding, I can fully understand why, when the 15th was around nearly everything was bonded (within reason, may I add, some people went way over the top) if in doubt bond, a few tenby earth clamps and a bit 10mm doesn't cost at lot in the average house. Seems now people are just getting more and more confused and doubtful as to bond or not to bond. lol
 
The more I read these threads regarding bonding, I can fully understand why, when the 15th was around nearly everything was bonded (within reason, may I add, some people went way over the top) if in doubt bond, a few tenby earth clamps and a bit 10mm doesn't cost at lot in the average house. Seems now people are just getting more and more confused and doubtful as to bond or not to bond. lol

Agree.
99% of the confusion results from a failure to understand the meaning of the terms 'extraneous conductive parts' and 'conductive parts' and that bondings only function is to prevent the possibility of a PD between the two. It doesnt help that bonding is always discussed/described in conjunction with the term 'earthing' when the purposes of bonding and earthing are entirely separate. It's a simple concept,and it never ceases to amaze me how many electricians still dont get it.
 

Reply to bonding of main water plastic incoming in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
800
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
983

Similar threads

  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
3K
If you can see a piece of plastic entering from the ground then (as cliff said), it does not need main bonding. I think (not sure) this is reg...
Replies
3
Views
448

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top