Just remove the main earthing conductor from the MET as if you were measuring Ze and test between that (the earth) and the pipe. No parallell paths then.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss bonding of main water plastic incoming in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Of course not, but SBSB said if the incomer is plastic then the PLUMBING isn't an extraneous conductive part. I would test the metal pipework nearest to the connection to the plastic incomer and if extraneous; bond.
Oops, sorry lol.
Haha............I was responding post 23 and the gem of a post 26 mate.
Megaflows and ADS etc.
Seems you don't need to Bond incoming services anymore as the neighbours will do it for you :shocked:
Obviously a windup................I hope !
Just remove the main earthing conductor from the MET as if you were measuring Ze and test between that (the earth) and the pipe. No parallell paths then.
If told to do it by the foreman do it and when questioned say that Mo Fo told me to do it!
That's assuming other services have been bonded, which if they have and it is affecting the water then bonding it anyway isn't going to do any harm. If the bonds are affecting the water so much that you get a 0.05 - 0.06 reading then some would argue that it would be safe to assume a bond is already in place and to leave it and crack on.
You miss the point mate,existing bonding has nothing to do with it. If a gas pipe (for example) is extraneous,it will be at earth potential or thereabouts whether it is bonded or not.There is likely to be some electrical continuity to the water system via mechanical connection between pipework at a boiler even with all bonds/earth disconnected. Thats why the IR test to establish whether bonding is required is nearly always misleading.....(IMO!)
A local firm in my area have just had the nic crawling all over them because they didn't run a main bond to the water main. Incoming pipe was plastic covered copper, rest of houses in plastic (scheme).
I would still run a bond and connect it on to the stop valve, this would satisfy the sheets, regs, and any electrician who looks at it.
The more I read these threads regarding bonding, I can fully understand why, when the 15th was around nearly everything was bonded (within reason, may I add, some people went way over the top) if in doubt bond, a few tenby earth clamps and a bit 10mm doesn't cost at lot in the average house. Seems now people are just getting more and more confused and doubtful as to bond or not to bond. lol
As this is new emerging technology and there is no common person know to it. But after it has happen, the conditions could be so different. Yet there is a little success but not enough to experiment publicaly.
Reply to bonding of main water plastic incoming in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net