Morning guys,
Thought I would throw one out there, on an eicr this morning and the main gas service comes in to a dedicated outbuilding separate from the main commercial building, the previous installers have run the bond from the met to the point of entry in a plant room, then from this point (seperate lugged cables) runs to the outbuilding to bond the gas again,
My gut feeling is they should be two seperate cables but looking for thoughts.
 
Morning guys,
Thought I would throw one out there, on an eicr this morning and the main gas service comes in to a dedicated outbuilding separate from the main commercial building, the previous installers have run the bond from the met to the point of entry in a plant room, then from this point (seperate lugged cables) runs to the outbuilding to bond the gas again,
My gut feeling is they should be two seperate cables but looking for thoughts.
Is it the same service?
You can use the same conductor for main protective bonds as long as it is continuous (your example is not) or, install another earth terminal so the disconnection of one does not affect continuity the other.
 
Is it the same service?
You can use the same conductor for main protective bonds as long as it is continuous (your example is not) or, install another earth terminal so the disconnection of one does not affect continuity the other.
Yes they are both the same gas main, but I agree if the bond at the plant room failed the external intake would not be protected
 
Yes they are both the same gas main, but I agree if the bond at the plant room failed the external intake would not be protected
Can you physically see the gas service where it passes between the buildings and if you can does it need two bonds?
 
Unfortunately not, it does go underground.
Got me thinking this and just looked in GN8 and Figure 5.13 which I think shows your set up ( they are supplied from the same DNO source?).
So I should say that bond should be continuous or connected in such a way the disconnection of one will not affect the other.
 
I will have a look at it later, but unless it quotes a Regulation it must be remember that GN8 is GUIDANCE Note 8.

As I said, unbroken main protective bonding conductors are generally accepted as good practice.
Fair point, out of all the Guidance Notes I find this one of the best.
 
This is making me think, as there is no Reference in BS7671 why is the Guidance Note showing it, is this why we have Safety Electrical Connection - Do Not Remove notices. My posts to the OP must be incorrect.
Does anyone have a recollection of any DNO insisting main bonds for PME systems must be continuous as this seems to be in the back of my head.
 
What else is in the dedicated building, any Electrical supply or is it just a Meter?
Yes it is just a meter building primarily, it does have the main tx in a seperate room to the gas meter but this room only has general small power and lighting but no electrical distribution and both rooms have separate external doors of which only the dno gave access to the tx.
 

Reply to Bonding Of The Same Service in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
354
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
905
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
https://www.edwardes.co.uk/products/mk-k1257whi-logic-plus-1gang-13amp-non-standard-dp-switch-socket?gad_source=1&gclid=EAIaIQobChMI7POp_pHFhgMVk5J...
Replies
1
Views
355
The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...
Replies
3
Views
613

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top