When rewiring a dwelling and installing a 17th ed board what bonding is required, main bonding, gas and water, supplementary? thanks
Last edited by a moderator:
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Bonding on a rewire in the Australia area at ElectriciansForums.net
Sure it's been asked many times, plastic supply pipe, stop cock under the floor, around a metre of copper then multiple plastic fittings etc etc. I'm not gonna install Main Bond to the water service, anyone think I should? Clearly I've done the gas.
Sorry should say if it's tns or tncs 16mm main bond 10mm to gas and water if it's tt only 6 mm to electrode