TNCS supply. New kitchen fitted two years ago. I'm fitting lights, but have noticed that there isnt any bonding from the gas bottles which supply the cooker. Should I be addressing this issue for the customer? Any advice appreciated.
 
sure others will advise better but i would have thought no bonding for bottled gas, unless its some strange UK reg.
 
It has to introduce an earth potential in order to require main bonding....not impossible but unlikely....you will be able to establish that on site.
 
Assuming we are talking here about red propane, free standing bottles stood at the side of the house then bonding is not required.
 
As a matter of interest, ...what type of feul/energy is being used for the central heating, ..if any??
 
Assuming we are talking here about red propane, free standing bottles stood at the side of the house then bonding is not required.

Surely this only applies if the pipe from the bottles doesn't go into ground. We have 4 x propane bottles for central heating and gas hob. the supply pipe (copper) goes into the ground then rises again before entering the house. This must make the supply pipe an extraneous conductive part.
 
Surely this only applies if the pipe from the bottles doesn't go into ground. We have 4 x propane bottles for central heating and gas hob. the supply pipe (copper) goes into the ground then rises again before entering the house. This must make the supply pipe an extraneous conductive part.

Yep........
 
Isn't this something you should be carrying out a test for? I'm sure I've read before that you're supposed to disconnect any earths that may be attached to the gas bottles/pipe work (earth from cooker ignition supply for example) then do a continuity test from the MET to the gas bottles/pipe work. If you get a reading of 33,000 ohms or less then it's classed as being an extraneous conductive part and requires bonding.

Wish I knew a reg to check against but I'm fairly certain this is the way to ascertain whether or not bonding is required in a situation like this. As a general rule though the cylinder won't pick up an earth potential unless there is buried pipework or the tanks aren't sited on a concrete base.
 
Isn't this something you should be carrying out a test for? I'm sure I've read before that you're supposed to disconnect any earths that may be attached to the gas bottles/pipe work (earth from cooker ignition supply for example) then do a continuity test from the MET to the gas bottles/pipe work. If you get a reading of 33,000 ohms or less then it's classed as being an extraneous conductive part and requires bonding.

Wish I knew a reg to check against but I'm fairly certain this is the way to ascertain whether or not bonding is required in a situation like this. As a general rule though the cylinder won't pick up an earth potential unless there is buried pipework or the tanks aren't sited on a concrete base.

You're close Dunc, you're looking for a value of 22KOhms or higher to consider the part in question to be a non-extraneous conductive part.

The figure is derived from a body resistance of 1000 Ohms and a current of 10mA (let-go threshold).
 

Reply to the thread, titled "bonding on gas bottles for cooker" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
bonding on gas bottles for cooker
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
georges,
Last reply from
IQ Electrical,
Replies
15
Views
9,296

Advert

Back
Top