I am doing some work for an engineering company who are taking over the unit next door. I have put in new 80A fused isolator feeding 3 phase board, this is supplying various 3 phase sockets, single phase lighting, 3 circuits along with 13A sockets. They have just had Propane heater installed, hanging from roof. I have put in separate 6A supply on fused switched spur as requested. I believe the 2” steel gas supply should be bonded as the tank is external, the problem is they have T’d the gas from the unit next door. Upon examining this other heater, installed 9 years ago I discover no bonding ! As both units have their own 3 phase supply with PME, My question is this: If I bond the new heater how will this impact the other unit ?
Is there an issue with potential differences using two neutrals ? I have not come across this problem before and would appreciate any assistance or advice from anyone with more experience in this field.
 
The common pipework (gas supply) must be bonded at its entry to each building, if you have Guidance Note 8 then figure 5.14 shows this detail.

I assume you are talking about main protective bonding to the gas service even though you mention 'bonding the new heater'
 
Yes, main protective bonding of gas service. I will check out Guidance note 8, thank you.
So from what you have both written I run an earth from earth point of supply to gas pipe at entry for each unit, bonding the pipe twice, from two different earth points ?
 
Yes, each building will be an equipotential zone so a bond is required from each main earth terminal to the point of entry to the building.

So 2 buildings, 2 main protective bonds.
 
Many thanks IQ,
2 buildings, 2 main protective bonds but gas pipe joins both so do the bonds not create one equipotential zone with two supplies ?
 
The pipework can introduce a potential from the building it exited to the building it enters-either earth or earth-fault so you need to create equipotential in each building.
 
Many thanks for your help IQ, sorry if it sounded like I doubted your posts, I just wanted to ensure I
had not been ambiguous in my wording.
Thanks again
Pat
 

Reply to Bonding question with two supplies. in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Article
This is an RSS feed of thread: Two electrical supplies and a single immersion element Content of the thread: Good afternoon, new joiner here with...
Replies
0
Views
147
Your kWh figures are giving you consumption averaged over each hour period, but don't give an indication of total instantaneous current. To try...
Replies
9
Views
901
Hello All, This is Vaithees from India. We are using an IR heater for a vacuum & non-vacuum chamber and got a heater from Chinese company and its...
Replies
0
Views
234
Given that a lot of EV's only charge from one phase when connected to a 3 phase chargepoint does the customer really need a 3 phase chargepoint...
Replies
1
Views
527
  • Question
Why not fit a self contained SPD fed directly from the Henley blocks, and free up a bay? Could probably make one up from whats there, using a...
2
Replies
47
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks