Hi chaps. I'll admit to being a bit confused about a bonding situation. A client of mine's incoming water supply is via plastic pipe. Now, an IR test between said plastic pipe and the subsequent metalwork (where the the copper pipe-work joins) gives a reading of >500M ohms, so confirming it's effectively insulated from earth (the metalwork that is). However, an IR test between the cold-water pipe-work and a known earth (actually the bonding clamp on the consumer's side of the gas supply) reads 0M ohms, thus implying that (at some point) the pipe-work of the water supply is bonded. Now, I can't verify where this may be; whether it's via the combi-boiler internal connection(s), or from a bonding cable I haven't managed to find. Net question being, as I can't currently (no pun intended!) assess the reliability of the water pipeworks bonding (i.e. I can't determine where it is!), do you guys think I should fit a new bonding cable and clamp regardless, to be on the (ultra) safe side? Or, as it's already at the same potential as the the gas metal-work etc., do I need to actually do so? (Sorry if this is a bit long-winded, just trying to be as descriptive as poss about the situation).
Thanks in advance for any advice!
 
No.
Bonding is required to eliminate any difference in potential, which may be introduced from outside the installation.
You have established that the water supply does not introduce a difference, so there is no point in bonding it.
 
I agree with the above, there are almost always a series of interconnections of metal water pipes and the electrical installation inside a property, this is not the issue.

To bond a piece of metal work that is not extraneous will only mean that there is another piece of metal that may be above earth potential during a fault and increase the danger not reduce it. In your case it would make little difference since there is already an interconnection but bonding for the sake of it is not safe.
If whilst doing a Ze measurement and had the main earth disconnected you were to measure resistance to the pipework from the disconnected main incoming earth this would give you more of an idea if the metal work were actually extraneous.
 
Now, an IR test between said plastic pipe and the subsequent metalwork (where the the copper pipe-work joins) gives a reading of >500M ohms, so confirming it's effectively insulated from earth (the metalwork that is).

Don't take this the wrong way, but are you connecting one probe to the plastic pipe and one to the metal?
 
That was my initially my goal, to to check that the plastic incomer was just that, i.e. a plastic pipe, and thus not introducing earth potential. And I wouldn't take any advice the wrong way fella, no worries
 
Thanks to all you guys for the advice, it's very much appreciated! (At least now I won't have to crawl around running 10M of 10mm Y&G behind some (very) old and somewhat manky kitchen cupboards!)
 

Reply to Bonding question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
463
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
673
loz2754
L
  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top