Hello guys I am going to show my ignorance now so please don't shoot me down in flames.
I have a guy who wants an extension to a circuit, he wants light and power to his garden shed.
He has an TN-S supply with an amazing 0.18 Ohms ELI.
16mm main earth conductor and old Wylex BS3871 MCB's.
He has had extensive work done to his house including many electrical installations, central heating, kitchen down lights etc.
The CU is in a cupboard under the stairs and has a solid concrete floor, many extensions have been added to his house.
After having all this work done I was disappointed to see he has no main bonding conductor to his water intake.
It has been completely neglected.
I have measured an R2 reading of less than 0.05 Ohms from the main water intake to the CU but I am guessing this is coming from the small CPC of the boiler supply cable and also the gas pipe bond (yes the gas pipe has been bonded) the boiler has also been cross bonded with the water pipes inside.
Now seeing as how this main bonding cable is so impossible to fit I was wondering if there was any way round it.
Is it possible to bond from the main water intake to the boiler which is a short run and then cross bond so that the gas pipe supplies the necessary low resistance path back to the consumer unit?
Basically using the gas supply pipe as a substitute to the main water bonding conductor.
I noticed another extension elsewhere in the house with a sink and someone has put a bonding clamp on the sink water supply pipe and connected a 6mm cable to it, I can only assume this 6mm cable is then terminated in a socket near to the sink as this bonding cable sure does not arrive at the consumer unit by itself, the socket that this bonding cable is connected to is a ring circuit back to the CU.
Using a gas pipe as a substitute to a main bond send shivers down my spine but I was interested to know what peoples thought are on this.
How flexible can we be with Bonding, does it have to be a cable that supplies the bond or can we use other means?
In an ideal world I would be able to run a 10mm bonding conductor from the main water intake back to the MET but this is not an ideal world.
Any opinions welcome.
Many thanks.
I have a guy who wants an extension to a circuit, he wants light and power to his garden shed.
He has an TN-S supply with an amazing 0.18 Ohms ELI.
16mm main earth conductor and old Wylex BS3871 MCB's.
He has had extensive work done to his house including many electrical installations, central heating, kitchen down lights etc.
The CU is in a cupboard under the stairs and has a solid concrete floor, many extensions have been added to his house.
After having all this work done I was disappointed to see he has no main bonding conductor to his water intake.
It has been completely neglected.
I have measured an R2 reading of less than 0.05 Ohms from the main water intake to the CU but I am guessing this is coming from the small CPC of the boiler supply cable and also the gas pipe bond (yes the gas pipe has been bonded) the boiler has also been cross bonded with the water pipes inside.
Now seeing as how this main bonding cable is so impossible to fit I was wondering if there was any way round it.
Is it possible to bond from the main water intake to the boiler which is a short run and then cross bond so that the gas pipe supplies the necessary low resistance path back to the consumer unit?
Basically using the gas supply pipe as a substitute to the main water bonding conductor.
I noticed another extension elsewhere in the house with a sink and someone has put a bonding clamp on the sink water supply pipe and connected a 6mm cable to it, I can only assume this 6mm cable is then terminated in a socket near to the sink as this bonding cable sure does not arrive at the consumer unit by itself, the socket that this bonding cable is connected to is a ring circuit back to the CU.
Using a gas pipe as a substitute to a main bond send shivers down my spine but I was interested to know what peoples thought are on this.
How flexible can we be with Bonding, does it have to be a cable that supplies the bond or can we use other means?
In an ideal world I would be able to run a 10mm bonding conductor from the main water intake back to the MET but this is not an ideal world.
Any opinions welcome.
Many thanks.