Just done an EICR and for a 3 phase board the tails were 35mm, but the DNO fuses were your standard 100A. Bonding conductors are 10mm. Any comments?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Bonding size in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
sorry just seen its bonding your talking about oooopsshould the earth tails not be at least 50% mm2 of the L N tails
bonding conductors need to be a min. of 50% of the required earthing conductor as determined by the adiabatic equation. the actual size of the main earthing conductor that is fitted is irrevelant as long as it is ≥ that determined by the adiabatic and complies with minimum size requirements.
On TNC-S (PME) systems, earthing/bonding conductors are based on the incoming Neutral conductor, not the phase conductor!!