Just done an EICR and for a 3 phase board the tails were 35mm, but the DNO fuses were your standard 100A. Bonding conductors are 10mm. Any comments?
bonding conductors need to be a min. of 50% of the required earthing conductor as determined by the adiabatic equation. the actual size of the main earthing conductor that is fitted is irrevelant as long as it is ≥ that determined by the adiabatic and complies with minimum size requirements.
That doesn't apply if TNCS. Adiabatic says 10mm is enough for the main earthing conductor.
Reply to Bonding size in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Hello all. I have been asked to fit a Ryefield board and switch-fuse on an existing 3 phase supply so that a shop can have its own meter and 3...