Hello all, first post so apologies if it’s in the wrong forum.
I wonder if someone could help me to determine if the bonding on a commercial district heating system is correct.
The gas boilers are situated in their own boiler house approximately 1000 meters away from a block of 12 storey flats; the heating and hot water to the flats are fed by underground steel district heating pipework; which then feed each flat by steel risers, entering each flat with a flow/return pipework with isolation valves fitted on each house entry, (Inside the property).
There is currently a phase of work being done to replace old Elson storage heating tanks with heat exchangers and alteration of copper pipework to the heat exchanger; the programme also includes removing 2 motorised valves and replacing the old programmer for a newer model which operates a valve on the heat exchanger to provide heating when required.
No additional wiring is being installed so a minor works cert is being issued for each property stating that all bonding is ok and the consumerunit is to the 17[SUP]th[/SUP] edition.
However; a dispute has occurred because I have said the steel pipework on the flow and return should be bonded in 10mm and link to the flow or return; but others are saying, not so because it is bonded in the boiler house which I assume would be a dead test as the steel pipework goes into the ground and is earthed, plus each property is not protected because no bonding from the consumer unit is fitted.
They have also said that on testing and the reading is below a certain level then the bonding is not required. This is the stumbling block, it does seem to me that a lot of steel in the block of flats are not bonded?
The water mains entering each property are bonded so I think the flow and return should also be bonded to each property.
Am I right or wrong?
I would really appreciate some advice as this could be a massive issue if I am right.
Thanks all.
I wonder if someone could help me to determine if the bonding on a commercial district heating system is correct.
The gas boilers are situated in their own boiler house approximately 1000 meters away from a block of 12 storey flats; the heating and hot water to the flats are fed by underground steel district heating pipework; which then feed each flat by steel risers, entering each flat with a flow/return pipework with isolation valves fitted on each house entry, (Inside the property).
There is currently a phase of work being done to replace old Elson storage heating tanks with heat exchangers and alteration of copper pipework to the heat exchanger; the programme also includes removing 2 motorised valves and replacing the old programmer for a newer model which operates a valve on the heat exchanger to provide heating when required.
No additional wiring is being installed so a minor works cert is being issued for each property stating that all bonding is ok and the consumerunit is to the 17[SUP]th[/SUP] edition.
However; a dispute has occurred because I have said the steel pipework on the flow and return should be bonded in 10mm and link to the flow or return; but others are saying, not so because it is bonded in the boiler house which I assume would be a dead test as the steel pipework goes into the ground and is earthed, plus each property is not protected because no bonding from the consumer unit is fitted.
They have also said that on testing and the reading is below a certain level then the bonding is not required. This is the stumbling block, it does seem to me that a lot of steel in the block of flats are not bonded?
The water mains entering each property are bonded so I think the flow and return should also be bonded to each property.
Am I right or wrong?
I would really appreciate some advice as this could be a massive issue if I am right.
Thanks all.