The major consideration here, which literary negates your choices whether to bond this staircase or not, is that it is already structurally connected to the buildings steelwork, probably at several locations!!!
So in answer to your question, like it or not, it's already inherently part of the buildings equipotential zone!!
'' How do you intend on creating an equipotential zone out side!!! ''
If, ....this building met all the weighting requirements for a lightning protection system to be fitted, which to be honest, is unlikely. ...The steel frame of this building will effectively act as the down conductors, and an appropriate number of the steel columns, will be roded, if not themselves suitably grounded... The outside staircase is already bonded to the buildings steel framework by bolted structural connections. There is no need for further bonding connections, Once the structural steelwork of the building has been bonded/connected to the electrical MET.
The requirements are the same for TN-S, TNC-S, TT when connecting Lightning Protection systems to electrical MET. Obviously, lightning protection and TTsystem earth rod positions are going to have to be outside of each others area of influence...
If the outside stair case is fortuitously connected or even bonded to the MET of the installation, this does not mean its within the equipotential zone of the installation. The problem with oustside is its very difficult to create an equipotential zone.
Chris