Hi am i reading it right that before you carry out any electrical work out in domestic properties that these pipes have to be upgraded to 10mm earthing cable even if they are already bonded but in less then 10mm
 
if bonding is in 6mm and no sign of damage, then it's generally acceptable to leave it, by calculating the min. size of main earthing conductor from the adiabatic, then the main bonding must be equal to or greater than 50% of that value.
 
Hi am i reading it right that before you carry out any electrical work out in domestic properties that these pipes have to be upgraded to 10mm earthing cable even if they are already bonded but in less then 10mm
No.
The minimum CSA for a Protective Bonding Conductor is 6mm², but where PME conditions apply 10mm².
In any event, the PBC must be at least half the CSA of that required for the main earth conductor.
Before conducting any alteration or addition, you are required to ensure the earthing and bonding arrangements are (if necessary for the protective measure applied for the safety of the alteration or addition) adequate.
Being adequate does not necessarily equate to compliance with the Regulations.
If the PBC is at least half the CSA of that required for the main earthing conductor, is 6mm² and shows no signs of damage or evidence of over heating, it is deemed adequate.
 

Reply to Bonding to gas and water pipes regs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I like your way of thinking.
Replies
6
Views
626
loz2754
L
During a new CU installation does the bonding for the gas and water also have to be upgraded to the latest regulations or just tested/ inspected?
Replies
0
Views
209

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top