Hello,

just a quicky. We have not done domestic in some time now.

We carried out a pir.

We found that the gas is bonded but the all other supplementary bonding is not in place.

now if there is a rcd coving the installation does the pipes ect need to be bonded?

As it is, there is no rcd so would I then give this as a option to bond the pipes/boiler or just install a rcd?


Thanks
 
nothing to do with whether RCD is fitted or not. if water comes in on metal pipework it needs bonding. code C2 if not. code C2 for no supplementary bonding in bathrooms if no RCD fitted.
 
No I understand if water comes in or gas ect I needs bonding. Gas and water has been earthed

I am talking about if supplementary bonding is required when there is no rcd? And if I install a rcd then they wouldn't be a requirement to install bonding to boiler bathroom ect?
 
Water supply will need bonding if metal service into property. Code 2 if it isn't. No supplementary bonding also Code 2. Covering bathroom circuits with an RCD is an option as long as all criteria are met.
 
Just a point mate it is now called EICR not PIR as you called it maybe a refresher course would be a good option if you are carrying out this type of work as the defect codes have no changed too
 
No I understand if water comes in or gas ect I needs bonding. Gas and water has been earthed

I am talking about if supplementary bonding is required when there is no rcd? And if I install a rcd then they wouldn't be a requirement to install bonding to boiler bathroom ect?

Yes. Supp Bonding is required when there isn't an RCD.
Yes if you cover all bathroom circuits with RCD protection and meet the necessary criteria to do so. You can omit supplementary bonding.
 
Is supplementary bonding perhaps NOT required in the bathroom?

Have you taken any measurements?

You cannot say yes or no by looking at it, let alone from a forum.
 
Supplementary bonding would only be required between simultaneously accessible extraneous and/or exposed conductive parts in the bathroom. Have you tested for these?

If there are indeed simultaneously accessible extraneous and/or exposed conductive parts in the bathroom then supplementary bonding is required between each in every circumstance unless all these three requirements are met:

1. The requirementsfor ADShave been met,2. All extraneous conductive parts are effectively connected to earth,3. An RCD with a rating not exceeding 30mA is provided for additional protection on all circuits within the bathroom.

Guess what... This doesn't mean that just whacking an RCD on will absolve the installer of any responsibility to abide by the requirements for supplementary bonding (as most 'electricians' these days like to think! [I understand that you are in this case the inspector and not the installer]).

If there are no simultaneously accessible extraneous and/or exposed conductive parts in the bathroom and no supplementary bonding then that warrants no code, if there are however and yet there is still no supplementary bonding then that is a C2. Whether or not adding an RCD to cover those circuits will mean that the requirements for supplementary bonding don't have to be met will be entirely dependant on your findings for the aforementioned points '1' and '2'.
This is basic and fundamental knowledge written in black and white thoughout BS 7671, in particular sections 415, 544 and 701, that anyone carrying out EICRs should have! The very fact that you are having to ask these questions causes me to doubt your level of competence to carry out what you are doing.
 
Supplementary bonding would only be required between simultaneously accessible extraneous and/or exposed conductive parts in the bathroom. Have you tested for these?

If there are indeed simultaneously accessible extraneous and/or exposed conductive parts in the bathroom then supplementary bonding is required between each in every circumstance unless all these three requirements are met:

1. The requirements for ADS have been met,2. All extraneous conductive parts are effectively connected to earth,3. An RCD with a rating not exceeding 30mA is provided for additional protection on all circuits within the bathroom.

All true.

However, there is also the fact that the installation may be such that the resistances between the parts may be sufficiently low that the requirements for bonding are met by the parts and cpcs themselves.

Depending on the situation, the required resistances can be relatively high.

In the OP's case there may be supplementary bonding outside the bathroom which has not been seen or the pipe work may not be extraneous.



Testing is the only way to find out - not asking "Do these pipes need boding?"
 
Although we see a lot of boiler and sinks in kitchens cross bonded, this is now not required(this i think was a 15 addition reg ) Supplementary bonding is required in a room containing a bath or a shower but if an the circuits within the bathroom are RCD protected then no Supplementary bonding is required
 
Refer back to me previous post, in partucular points 1,2 and 3 Flanders :)

Just because the bathroom has an RCD, it doesn't automatically mean it no longer requires supplementary bonding.
 
This freezing forum caused me to lose my post which was going to refer Flanders to post 10 by D Skelton
He has now been admonished by the Author of that post 10 and rightly so

This forum is also getting spammed again
 

Reply to Bonding to pipes in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hi I need help with understand supplementary bonding. I know RCD is additional protection and in the even of the fault at leakage of 30mA, it...
Replies
0
Views
37
  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top