cymroaur

Hi all,

Been to look at a job in a chalet. Nice shiny 16mm earth from the CU to an earth terminal, sh**e 4mm oxidized to f*** from the terminal to the armour of the incoming, looped to the 'loop out' SWA going onto the next chalet (sorry, didn't take a photo). Anyway, the site owner has said that maintenance crew will be onto it within a few days, which the customer reckons will be next year! So in the spirit of getting the job done quickly, he's asked if I could do it. So my question is: What's the best way of attaching to the armour, without having the cable loose to slip a gland over it. Jubilee clip? Earth strap? Is there a product out there which I don't know about?

P.S. The property is empty for a couple of weeks, so have switched off for now.

Thanks in advance.
 
If it must be done with the feed to other caravans left live, then constant tension springs are the way to go with this I think. Strip the sheath off the SWA and then wrap the spring once around the armour. Insert the end of your new earthing conductor onto the spring and then continue wrapping the spring around. I sometimes double the conductor over 2 wraps to ensure a good contact. Then seal the whole lot with self amalgamating tape.
 
Is this a DNO or private installation.... Taking it as private, you can provide a ''constant pressure spring'' earthing point with a braided earth conductor to the SWA. Do not, and never use a ''jubilee clip'' direct to the steel wire armouring, relying on the cable bedding and insulation if tightened to excess now, or in the future by others.....
 
These "Constant force springs" have obviously passed me by. My cable jointing experience was a very long time ago but you are never too old to learn. I can think of a particular application of these devices that would have saved me a lot of time and money.

Thank again for the post
Phil
 

Reply to Bonding to SWA armour - not able to gland in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
839

Similar threads

I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
893
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top