I've not yet got a copy or read the 18th ed
But I heard the other day from a young Engineer at work who's doing the course ( his first time doing regs exam) that in the 18th it's compulsory to bond all joins in tray etc

Can anyone elaborate on this?
 
Yes I thought it might be ...

When he mentioned it I asked him what had changed in regard to this , he just said it was a new requirement and in future we'd probably have to do it.

To be fair he's never used BS7671 so I did think that maybe he's mistaken.

In the job I do, we run tray fixed to steel box section frames (powdercoated) and generally it's the customers responsibility to ensure bonding is suitable to that particular countries regs


ie in China and India they do nothing, but other countries have varying amounts of bonding to frame and tray

One company insists we link every single join in tray and bond repeated intervals to all steelwork so in view of this it's always agreed in the contracts that all power supplies and bonding are carried out by a local contractor
 
Usually there is no need to either earth or bond traywork. If the cabling is insulated and sheathed, Class 2 equivalent construction, the traywork won't be an exposed conductive part so no earthing required. Traywork doesn't usually introduce an earth potential that isn't already present, so no bonding required.

That being said, inspectors love to snag traywork which isn't earthed or bonded.
 
Heard that argument a couple of times!

One firm I worked with had us go round checking all the tray on a big job with a long lead and test to show the Clerk that the tray continuity was ok , potential to earth was no worse than sll the metal work around the place etc and that bonding at couple of points was sufficient

Still ended up having his way and bonding every thing even after a Chartered Engineer agreed that it wasn't needed
 
It makes me wonder what the world these clerks of works and electrical consultants live in the other day I was doing some testing with a contracts manager and the consultant asked if the classroom sink needed bonding they still have in some of these specs about bonding window frames and suspended ceilings.
 
I've not yet got a copy or read the 18th ed
But I heard the other day from a young Engineer at work who's doing the course ( his first time doing regs exam) that in the 18th it's compulsory to bond all joins in tray etc

Can anyone elaborate on this?
Yes true ,it has to be continuous any cut in the tray will hinder that hence you put another link to make it continuous.
 
Can anyone quote the Reg. No. that requires tray to be bonded?
Would probably help if we knew whether the tray is extraneous or an exposed conductive-part.
 
Cables are insulated and sheathed so not an exposed part

Any earth potential is the same as the metal framework and walls that the tray is attached to

So I would say it's neither exposed or extraneous
 
In this case the whole structure is one big faraday cage
Even where tray joins are bolted together I think there's enough surface area clamped together or fixed to brackets which are fixed via tapped holes all along the length of runs to make the continuity consistent .
 
I'm going to suggest we test it properly to determine as it's not really black and white whether it does need doing or not
Its all down to how different people decipher the reg
In my post before I said it was neither but it can be argued either way
 
Well does it introduce a potential to the location it serves?
Is it in good contact to an outside earth at true earth potential?
I doubt it’s going to be extraneous but then I’m not on site.

Is it an exposed conductive part ie does it form part of the electrical installation or is it mearly a support system for the cables ?
 
Well does it introduce a potential to the location it serves?
Is it in good contact to an outside earth at true earth potential?
I doubt it’s going to be extraneous but then I’m not on site.

Is it an exposed conductive part ie does it form part of the electrical installation or is it mearly a support system for the cables ?
It is a safety precation,it might introduce potential depending on wher and how it is istalled.
I thought by bonding it you are establishing contact with the outside earth
 
It is a safety precation,it might introduce potential depending on wher and how it is istalled.
I thought by bonding it you are establishing contact with the outside earth
Bonding randomly can create its own hazards
Often when installed the tray supports are fixed to say the metallic structure of the building so are connected to earth that way if the structural frame is bonded by being an extraneous conductive part
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

edexlab

Arms
-
Joined
Location
Uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Bonding tray in 18th edition
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
19

Advert

Thread statistics

Created
edexlab,
Last reply from
Toneyz,
Replies
19
Views
4,112

Advert

Back
Top