Hi i am doing a property atm a periodic and its got 6mm bonding obviously it needs 10mm but does it need upgrading i think it will be a code 3 etc iand cross bonding between the boiler pipes?, and if it has 16mm tails instead of 25mm on 100A fuse but i cant replace these without concerning the dno. Thanks for your advice just didn't know how far i should go with this
 
Last edited by a moderator:
hi mate old properties used to have 16mm tails depends on the load now, cross bonding between pipes is old too, depends on the db and earthing
what are you doing?
:) if it all comes into the regs then fine have you checked zs and ze
 
Last edited:
For a PIR if you calculate the earthing conductor size using the adiebatic equation and all is good and as said the Ze and Zs results are satifactory it will be a code 4 as in does not comply with BS7671:2008
 
Last edited:
Code 3 means 'requires further investigation'.....if you know the bonding conductor size it wont requiire further investigation.The minimum sze of the main bonding conductor will depend on the earthing system....6.0mm will be adequate on a TT.
Suggest you have a close look at bonding requirements in the BRB and OSG before recommending 'cross bonding boiler pipes'.
 
Main Earthing Conductor

The minimum csa of the main earthing conductor must be determined by the adibiatic equation or selected from Table 54.7 543.1.1.
If the adibiatic equation is used, the minimum csa of the main earthing conductor must be 6mm 544.1.1.
Table 54.7 suggests a 16mm main earthing conductor for phase conductors with a csa of up to 35mm.
The csa of the main earthing conductor where PME conditions apply should be not less than that for a main protective bonding conductor (10mm) for the same installation 544.1.1.


Main Protective Bonding Conductors

For TN-S or TT systems the csa of main protective bonding conductors must be a minimum of 6mm and not be less than half the csa of the main earthing conductor.
544.1.1
For a PME system the csa of the main bonding conductors must not be less than that given in Table 54.8 ie a 10mm protective bonding conductor for a neutral conductor of 35mm or less. 544.1.1
 
yeah thats what i thought as an electrician did a pir on a property and said the boiler pipes need cross bonding and upgrading the earth but its all rcd protected so didn't see the need just wanted to check to make sure. you are saying that you don't need to cross bond the pipes anymore whats the logic behind this?? Thanks
 
yeah thats what i thought as an electrician did a pir on a property and said the boiler pipes need cross bonding and upgrading the earth but its all rcd protected so didn't see the need just wanted to check to make sure. you are saying that you don't need to cross bond the pipes anymore whats the logic behind this?? Thanks

There was never any logic to it....it was just a myth.
 

Reply to Bonding in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
74
  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
389
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
352

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top