Hi all. I'm wiring a flat (new installation) there's no gas pipe, water main is plastic and all other pipes were too. Just gone back to second fix and found the boiler cupboard full of copper pipes ! I would have bonded these had I known they were going to be there, do i have to or wil it be ok as everything is RCD protected ?
 
get a long test lead, do an IR test at250v between MET/ CU earth terminal, and the copper pipes. if your reading is over 23kohms, no need for bonding. what fuel is the boiler?
 
Last edited:
testing between the met and the pipes, or any extraneous metalwork and met to identify if supp bonding is required,.

as you said earlier the boiler pipes do not need to be bonded together (although plumbers will argue different as its in there training that it is required)

however if you wanted to provide supp bonding for whatever reason to whatever part but were not sure if it was needed then carrying out an ir between the pipe and a known earth would identify this.
 
Last edited by a moderator:
Hi there. Imagine scenario: Heavy rain outside, boiler flu trough the aloy roof with lead flashing on flue. Copper guttering, and Tv antena cable passing close bay all the way down to the ground. Bonding opinion.!!!???
 
If there are no extraneous parts that require main bonding....and the boiler is not in a special location as defined in the BRB....there is no requirement to supplementary bond the pipes...But...if copper pipes from the boiler enter a special location and the 3 conditions to omit supplementary bonding are not met,the pipes will require supplementary bonding at the point of entry to the special location...or....if the pipes are electrically continuous this may be more conveniently installed at the boiler!
 
Thanks chaps, Wirepuller, very concise ! that does it for me. The boiler is in a cupboard which is in a bathroom and there's a towel rail plumbed through the wall of the cupboard. It's an electric boiler btw
 

Reply to Bonding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
764
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

Similar threads

  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
3K
If you can see a piece of plastic entering from the ground then (as cliff said), it does not need main bonding. I think (not sure) this is reg...
Replies
3
Views
445

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top