Well, ...if all your panels go into Ex Zone 1 hazardous areas, then all terminations should be of the enhanced Ex spring loaded variety, where ferrules/flat spade crimp terminations are as far as i know, compulsory. I don't tend to work with the European EX systems, i am far more conversant with the American hazardous systems, which i use quite regularly...

No-ones having cheap digs, you're the one that wrote the aforementioned post, no-one else, we can only go by what you write/post, we're not mind readers either!! Don't blame me for not assuming you meant to insert an IF, as the rest of your post clearly sounded as if you considered ferrules and the like, as not being necessary and didn't enhance connection security.
 
"No-ones having cheap digs, you're the one that wrote the aforementioned post, no-one else, we can only go by what you write/post, we're not mind readers either!! Don't blame me for not assuming you meant to insert an IF, as the rest of your post clearly sounded as if you considered ferrules and the like, as not being necessary and didn't enhance connection security".

Well try reading all of my posts next time instead of jumping to conclusions mate...........post 32 onwards made it clear what I was talking about .........or did you not read the rest ?

I've been doing installs on Hazardous area stuff for nigh on 40 year and am well aware of the requirements thank you very much.........................still a bloody minefield mind you when your kit is going to different countries with different regs etc!
I tried for 2 hours to explain the concept of 'Increased safety' to a Korean client the other week............nightmare !

 
I'm not getting into one here, but you only cleared things up After my comments, (Post 32 clears nothing up) so it's nothing to do with reading all your posts as you put it, as i can't read what hasn't been posted up to that time!! Oh and if you look again at my post 41, you'll see a lol!! and a :smiley2: at the end of the post!!!


As for Korean's, been working with them for more years (off & on) than i care to remember. The only time you ''Know'' that they have understood something you are telling them, is when you see a big smile (or frown) and a long Ahhhhhhhh, that sounds more like a Orrrrrrrrrrr!!. That's when you know the penny has finally dropped!!
 
Fair enough no probs here.

Must admit when trying to explain stuff to Korean/foreign clients I shouldn't complain when they can't grasp what I'm telling them.

I mean.........explaining the difference between EXd and EXe to a Korean in a broad Geordie accent lol.
Poor guy has no chance :confused5:
 
Fair enough no probs here.

Must admit when trying to explain stuff to Korean/foreign clients I shouldn't complain when they can't grasp what I'm telling them.

I mean.........explaining the difference between EXd and EXe to a Korean in a broad Geordie accent lol.
Poor guy has no chance :confused5:


I'm pretty sure the Koreans will be using the Americain NFPA 70 (NEC Code) etc, which categorize hazardous areas into Class/Divisions/Groups, and can be quite different to the European Ex system, as in what measures of protection etc is required. Not sure if you have worked to the Yank system or not, but have included a rough guide as to how such areas would be categorized...

North American hazardous locations classification in classes, divisions and groups

In general hazardous locations in North America are separated by classes, divisions, and groups to define the level of safety required for equipment installed in these locations.


Classes

The classes defines the general nature of hazardous material in the surrounding atmosphere.

Class
Hazardous Material in Surrounding Atmosphere

Class I
Hazardous because flammable gases or vapors are present in the air in quantities sufficient to produce explosive or ignitable mixtures.
Class II
Hazardous because combustible or conductive dusts are present.
Class III
Hazardous because ignitable fibers or flyings are present, but not likely to be in suspension in sufficient quantities to produce ignitable mixtures. Typical wood chips, cotton, flax and nylon. Group classifications are not applied to this class.

Divisions

The division defines the probability of hazardous material being present in an ignitable concentration in the surrounding atmosphere.
Division
Presence of Hazardous Material

Division 1
The substance referred to by class is present during normal conditions.
Division 2
The substance referred to by class is present only in abnormal conditions, such as a container failure or system breakdown.

Groups

The group defines the hazardous material in the surrounding atmosphere.
Group
Hazardous Material in Surrounding Atmosphere.

Group A
Acetylene
Group B
Hydrogen, fuel and combustible process gases containing more than 30% hydrogen by volume or gases of equivalent hazard such as butadiene, ethylene, oxide, propylene oxide and acrolein.
Group C
Carbon monoxide, ether, hydrogen sulfide, morpholine, cyclopropane, ethyl and ethylene or gases of equivalent hazard.
Group D
Gasoline, acetone, ammonia, benzene, butane, cyclopropane, ethanol, hexane, methanol, methane, vinyl chloride, natural gas, naphtha, propane or gases of equivalent hazard.
Group E
Combustible metal dusts, including aluminum, magnesium and their commercial alloys or other combustible dusts whose particle size, abrasiveness and conductivity present similar hazards in connection with electrical equipment.
Group F
Carbonaceous dusts, carbon black, coal black, charcoal, coal or coke dusts that have more than 8% total entrapped volatiles or dusts that have been sensitized by other material so they present an explosion hazard.
Group G
Flour dust, grain dust, flour, starch, sugar, wood, plastic and chemicals.


The specific hazardous materials within each group and their automatic ignition temperatures can be found in Article 500 of the National Electric Code and NFPA 497/ NFPA 70E.
Group A, B, C and D apply to class I locations. Group E, F and G apply to class II locations.


Temperature Code


A mixture of hazardous gases and air may ignite in contact with a hot surface. The condition for ignition depends on several factors as surface area, temperature and concentration of gas.


Equipment approved, receives a temperature code indicating the maximum surface temperature of the equipment.

Temperature Code
Maximum Surface Temperature
[SUP]o[/SUP]F
[SUP]o[/SUP]C
T1
842
450
T2
572
300
T2A
536
280
T2B
500
260
T2C
446
230
T2D
419
215
T3
392
200
T3A
356
180
T3B
329
165
T3C
320
160
T4
275
135
T4A
248
120
T5
212
100
T6
185
85

Equipment that does not exceed a maximum surface temperature of 212 [SUP]o[/SUP]F (104 [SUP]o[/SUP]F ambient temperature) is not required to be marked with a temperature code (NEC).
 
Yup have sent stuff all over the world at one time or another.

I seem to remember one job ( gulf of mexico I think) where they wouldn't accept Intrinsically
safe equipment as they didn't recognize the concept !

Twas a few year back so my memory might be fuddled a bit with the detail lol
 
Yup have sent stuff all over the world at one time or another.

I seem to remember one job ( gulf of mexico I think) where they wouldn't accept Intrinsically safe equipment as they didn't recognize the concept !

Twas a few year back so my memory might be fuddled a bit with the detail lol


That's strange, as Intrinsically safe equipment has a UL standard (UL 993) that certainly isn't a million miles away from that recognised in Europe!! Mind there has been revision to UL 993 very recently (2012), so there may have been a conflict, though i doubt it. Anyway as there has always been a Standard related to Intrinsically safe equipment, i can't see how they can state they don't recognise the ''concept''... lol!!
 
gulf of mexico's the clue. a bunch of texans and wet-backs, collective intelligence below that of your average goldfish.
 
That's strange, as Intrinsically safe equipment has a UL standard (UL 993) that certainly isn't a million miles away from that recognised in Europe!! Mind there has been revision to UL 993 very recently (2012), so there may have been a conflict, though i doubt it. Anyway as there has always been a Standard related to Intrinsically safe equipment, i can't see how they can state they don't recognise the ''concept''... lol!!

Well when saying they didn't recognize the concept it may well have been that their spec on that particular job just wouldn't allow it.................few year back now but can still vaguely remember the hassle it caused at the time.
 

Reply to Bootlace Ferrules in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
800
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
983

Similar threads

I’m sure I’ve seen an LSF round cable used on sites before as well with an insulated earth. Not flex, something a bit more substantial but not FP...
2
Replies
21
Views
4K
  • Question
There is nothing inherently wrong with this part of the layout. There is another option that you may want to consider. Those supply conductors...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top