borrowed neutral | on ElectriciansForums
Discuss borrowed neutral in the Talk Electrician area at ElectriciansForums.net
A
aaronstuart
Sorry for this dumb question....
What would be the easiest way of testing to see if you have a borrowed neutral?
Disconnect neutrals in cu and do a continuity test between neutrals?:confused:
My apologies in advance....
sorry for the short answer earlier ;with continuity you're trying to prove which circuit /s the neutral is on .
never checked your profile so i assume you know what i mean !!
so if you disconnect all neutrals at cu then connect on neutral of upstairs lights and neutral of downstairs lights, thats how to find it?
If you are concerned about a possible shared neutral to the landing light from the upstairs circuit switch off all the lighting breakers with the landing light ON.
Disconnect the downstairs live and the upstairs neutral, if you have continuity between them you have a shared neutral somewhere.
Reply to borrowed neutral in the Talk Electrician area at ElectriciansForums.net
Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Found the cause of the tripping…. Just jointed them through… all clear now. Removed the smoke detectors completely. They were due to be...