I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but using the same socket it kept tripping the rcd. Socket next to it worked okay.
Replace double socket with a new one. At the same time ran an earth wire to the metal box.
Retested. 1 ohm earth and rcd trip current now 1140ma. Removed box ground wire and rcd trip point back to 18ma. Same as the other double socket.
Incoming has earth to neutral.
Screws in faulty outlet were not very tight.
On removal the two faceplate screws were black.
Socket had 4 pairs terminated in it??
Any suggestions of where else to look?
Replace double socket with a new one. At the same time ran an earth wire to the metal box.
Retested. 1 ohm earth and rcd trip current now 1140ma. Removed box ground wire and rcd trip point back to 18ma. Same as the other double socket.
Incoming has earth to neutral.
Screws in faulty outlet were not very tight.
On removal the two faceplate screws were black.
Socket had 4 pairs terminated in it??
Any suggestions of where else to look?