Has anyone used a brass gland plate to earth a line of SWA glands e.g. at a DB, and had anyone such as an NICEIC inspection flag it up as non-compliant?

I am proposing to screw a flat plate of brass onto the top of the DB and mount the glands through it with their usual locknuts, A brass bolt through the plate will take the lug of a cable running to the earth bar. I consider this to be a suitable way to earth the glands, but someone else is saying that they did something similar and their NIC man pulled him on it and demanded separate banjos or piranhas with individual flyleads.

Any thoughts?
 
Nor me - except - a pedant could argue that if when you open the packet of SWA gland and find a banjo (as you do) then 'that's how the manufacturer intends.....'.
 
In some ways it's better - fewer connections to maintain.
their NIC man pulled him on it and demanded separate banjos or piranhas with individual flyleads.
Might be a distinction between using armour as CPC and simply earthing the armour? A single cable to earthing bar from plate may have not met collective requirements for a group of CPCs.
 
Someone like to confirm what that is?
Don't have BBB with me, Section 543 (can remember that nice number!) covers sharing cpc's somewhere in it - something about the highest current expected from a fault on one of the circuits. Requirements for minimum CPC size in general (as separate) need to be met too. Probably no more than you were going to do anyway.

I was more trying to convey that knowledge of CPC sharing can be sketchy as it isn't common and anything that looks unusual can easily cause an assessor to spit dummy out.
 
543.2.9 suggests this is OK to me, although I guess easily confused with 543.2.7
 
Cant see anything wrong with it, myself. Once fitted, it's solid, less complicated, room saving, easier and it's fixed to, and therefore part of, the metal enclosure. With the earth bar link, extremely satisfactory.
 
Right, good, logic prevails.
Now, supposing the plate were not brass but aluminium?
Or steel, even?
Installed hundreds of pyros into industrial boiler and heating control panels in the past.. without the earth tailed pots, sometimes in groups of 20, 30 or more. Imagine the work involved to banjo or even extend pot tails.
If a problem with the NICEIC, it could be just a case of regulation for today's class of workfolk and materials.

In some extreme situations, maybe one issue could be the adverse affect of different metals but, in general....? Then again, another plus point.......brass or ally wouldn't have the rust factor.
 

Reply to Brass gland plate for SWA in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
952
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top