The trip ratings of upstream and downstream circuit breakers should be same as I was told by a senior. Why cant the downstream circuit breaker be rated less than the upstream breakers. I'm not talking about the short circuit ratings, but the Ampere trip rating.
 
I haven't got a clue what this senior figure is on about, the fact you have to try to achieve short circuit discrimination against upstream devices automatically means that the upstream device will be rated much higher, it sounds like they haven't a clue what they are talking about.

If you can achieve full discrimination then a supply to a standard mcb board would usually require a 160amp rating to achieve this, running the same size ratings whether the trip curve is different or not will not achieve this in any way.
 
I will just add a note here as I just realised you are from Saudi Arabia...

Please note that the forum is based around the BS 7671 and other British Standards so our replies may not reflect local regulations if you are not UK based.
Having said this, discrimination works the same regardless of borders, how each country regulates to account for discrimination and what is required is up to them though, if you are confused or concerned by the information given to you then you should seek relevant information/regulations for your country.
 

Reply to Breaker Coordination in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
865

Similar threads

I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
695
sounds like one of those jobs to swerve and let it be someone else's problem
Replies
12
Views
924

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top