Breakers & Cable Sizes | on ElectriciansForums
Discuss Breakers & Cable Sizes in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
hpmuk
Evening all,
Currently studying Electrical, quick question.
Is there a page in the onsite guide which tells you the minimum size per breakers ??
Thanks in advance
not exactly. the rating of the breaker must be less than the ccc of the cable. e'g if your cable max. amps is 9A, you would fit a 6A breaker.
The minimum cable size should always have a higher CCC than the circuit protection device, then the cable size itself is subject to cable calcs to determine its required csa.
To Note! there are a few excemption in the regs where this is not the case but overall this is the rule.
Reply to Breakers & Cable Sizes in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
N
He hasn't provided any certificates, including previous work. He sends invoices when he needs paying.but no vat registration number etc on...
  • Nessab16
  • Ireland
  • 8
  • 515
Nessab16
N
Sort of; technically speaking the 10mA is required to hit the 40mS target at 50-149mA, whereas the 30mA device can be happily snoozing along for...