Hi,

Im getting a Ze reading of 580 ohms on a TT installation, the existing earth to rod is either a 2.5 or a 4mm and im not sure of the route.

My question is if I run a 10mm earth (approx 35m) how much will it bring down the Ze?
 
Does the Ze have to be under 200 ohms on a TT guys?

No but it has to be stable and that is generally accepted to be around 200 Ohms, meaning that degradation due to drying and freezing of the soil will struggle to push the value to an unacceptable level.

I always say this but give me a deep rod at 400 Ohms any day rather than a shallow one at 200 Ohms, depth is king!

If you work out the resistance of 35M of 2.5 6491-x you'll see that 99.9 % of your reading is the rod itself so that's where you need to concentrate your efforts.
 
Last edited:
I think you have what is called in the trade a right pig of a job .......................

Without seeing the install you have hobson choice really, go deeper with the one in the conservatory, which is unbelievable that you would build a conservatory around an earth rod, which might explain why you have such a poor reading, or find another location and try to fit another electrode(s)
 
Hi,

Im getting a Ze reading of 580 ohms on a TT installation, the existing earth to rod is either a 2.5 or a 4mm and im not sure of the route.

My question is if I run a 10mm earth (approx 35m) how much will it bring down the Ze?

One question, why are you running a 10mm2 earth conductor?
 
No but it has to be stable and that is generally accepted to be around 200 Ohms, meaning that degradation due to drying and freezing of the soil will struggle to push the value to an unacceptable level.

I always say this but give me a deep rod at 400 Ohms any day rather than a shallow one at 200 Ohms, depth is king!

If you work out the resistance of 35M of 2.5 6491-x you'll see that 99.9 % of your reading is the rod itself so that's where you need to concentrate your efforts.



my wife keeps telling me its the depth of the rod that counts lol
 
Also may be worth a call to the DNO and see if there is a PME available somewhere.

That would be the best solution possible, if it's available and well worth a shot, that's for sure!! lol!!


Unless your installing a bare copper cable at least a metre deep, then forget it, it ain't gonna do a thing for you. The BRB says a 200 ohm Ra is good, ...I do not!! You need to go for as low a value as you can. The deeper you go the better your Ra is going to be, and will be stable. Remember, that first metre is going to be prone to seasonal weather conditions, so when frozen or bone dry, that first metre of rod may as well not be there.

Forget this existing rod in the greenhouse and and install/drive-in 2 or 3 extendable rods (min 5/8'' rods) Nothing to stop you connecting accross to the existing rod, but it being at over 500 ohms pretty pointless!! ... Test them, and if necessary use chemical ground rod enhancement, to increase the ground conductivity.

Unfortunately there's a bit more involved in creating a TT installation, than bunging in 1.2 m 3/8'' rod willy nilly and expecting it to provide a stable decent Ra value.
 
Last edited by a moderator:

Reply to Bringing down Ze? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
175
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
1K
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top