optician
Friend of mine has a rental property that has just had a British Gas electrical Inspection.
Its a Tns, 30 mA main switch.
Its an old installation.
The Main earth cable is under size and to an earth clamp on the sheath of the main supply cable
The Bonding is also under-size and also to an earth clamp on the suppliers cable.
There is no earth in the lighting system.
So its not right.
But no one is adding or altering the electrical system.
I am pretty sure he has only done a visual check and has given a report saying the bonding needs
replacing/updating, ok, don't have a problem with that. And rightly has said no metal lighting accessories.
But then has stuck a sticker on the Consumer unit saying essential electrical cable is missing and that no electrical equipment should be used until this matter is addressed. (if i remember the sticker correctly)
I'm not sure that placing this sticker is warranted(which is why I'm writing this) can Anyone clarify
for me please.
Its a Tns, 30 mA main switch.
Its an old installation.
The Main earth cable is under size and to an earth clamp on the sheath of the main supply cable
The Bonding is also under-size and also to an earth clamp on the suppliers cable.
There is no earth in the lighting system.
So its not right.
But no one is adding or altering the electrical system.
I am pretty sure he has only done a visual check and has given a report saying the bonding needs
replacing/updating, ok, don't have a problem with that. And rightly has said no metal lighting accessories.
But then has stuck a sticker on the Consumer unit saying essential electrical cable is missing and that no electrical equipment should be used until this matter is addressed. (if i remember the sticker correctly)
I'm not sure that placing this sticker is warranted(which is why I'm writing this) can Anyone clarify
for me please.