drywax
I've been to a ladies today who has a maintenance contract with B Gas £50 a month not sure what it covers but they went around pat tested the appliances and condemed the boiler. So the next day a surveyer popped around to quote her for a new boiler,. like for like replacement on a FCU, and said that they couldn't do the work because there was no main earth present?
now surley this has nothing to do with the work they carry out and if the customer says they don't want to pay for a spike to installed then thats upto them.
Now this is the bit that made me chuckle popped my head under the stairs and she's got a TNCS or PME gas is bonded in 10mm, water is bonded to lead in 6mm under the floor boards.
I told her to ring her DNO just to clarify her supply type then ring B G back and complain if I was correct
I then said at the worst case scenario I would upgrade the water bonding for a nominal fee.
Any one had similar experience with the these jokers