Hi
I have a broken neutral in a socket ring, the customer doesn't want it fixed as he intends to re-wire the property in 18 months time. I have changed the consumer unit. Should I refuse to issue the certificate or put it in the notes. He has energised the circuit despite my advice not to.
 
What about the neutral fault is it still in circuit.

If you removed the faulty leg then down rating the MCB that would be a satisfactory solution.

If you have replaced the CU and you have a non compliant circuit you can not connect it and put it back in service.

If you left the circuit disconnected and made suitable comments on your cert and the coustomer chose to reconnect himself then there is not a lot you can do. But cover your self by stating circuit ??? Left dicconnected due to open ring fault.
 
Last edited:
Ah you are quite right steveberry,I forgot about the neutral fault, that leg of the circuit needs to be disconnected , by tracing the legs of the ring main to find that leg to disconnect you could make 2 temporary radials and still report that on the cert. By doing this you might with a bit a luck come across the broken neutral anyway.
 

Reply to Broken Neutral in Ring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
832
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
930

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top