Attended a seminar today based on EV charging points. The broken PEN conductor was mentioned and converting to TT.

2 things.
1. How often does a PEN conductor go down?? My understanding was that they use PME to reduce this risk further.

2. I asked the question as to should we be installing class 1 external light fittings / exterior water taps (no plastic joints) on a tn-c-s setups with the same potential to become live in the event of a broken pen. I honestly dont think they knew how to answer it. They just fobbed me off. So am i missing something?? Surely the risk is exactly the same. We dont go and TT mrs smiths metal light fitting beside her front door??
 
I'll put money on it being in one of the amendments.

You're right though, should be done by the DNO, but I believe the reason it was included under the electricians scope of work, is to try an save money for the DNO who is already struggling to just maintain our national grid shovel enough money into the shareholders grubby mitts.

FIFY
 
So what are we actually looking at ? When we come across a faulty PME

Lost/deteriorating N connection somewhere in the ground ? Or problems back at the sub station

Has anyone ever measured the touch voltage on a tingly tap during one of these faults

My thoughts too. I see Essex comment of 1 a day. Thats much higher than id have thought tbh. Interesting stat. I dont know of any incidents my way.
 
My guess is that if you find it and it's not in the news, then it's a local issue with a failed joint. If it's a failed neutral at the substation then it stands a good chance of making the local (or even national) news.
I confess to access to a little inside knowledge about goings on in my local DNO - and they are in a difficult position. As we all know, most substations are out in the open, and once down to the 11kV-415/240V local level are in practical terms unprotectable. Thieves will nick anything even if it is bolted down and typically without any appreciation of the risks they face or care for the problems they cause. On top of that, if someone does injure themselves, the HSE are on the case asking why they (the DNO) allowed it to happen :rolleyes:
In the link above, someone nicked a few feet of neutral cable. I recall a similar case in Lancashire not that long ago where most houses in a whole street had similar issues when a neutral link was stolen from the exchange.
Things I've heard from my insider include a whole earthing grid ripped out from a 132kV substation; and them getting a cooling alarm from a substation, and the engineer arriving to find the last of the oil disappearing into the ground thanks to some **** having nicked the brass valve off the drain point.
 

Reply to Broken PEN conductor in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
494
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
972
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
454
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top