P
parm
Working in a 2 bed terrace and been asked to do a pir, the continuity on the downstairs ring final is confusing me and wondered if one of you chaps with a fresh pair of eyes could help me out. End to end continuity of Rn is open end to end of R2 is open but I'm getting a low fluctuating reading for R1. I've narrowed it down to 2 sockets which appear to be both the start and the other the end of the ring final and it's between these two sockets where I'm getting these readings. The wiring was done by professional type diyer fate a fire in the property a few years ago and the owner suspect not all the wires wire replaced. I could split the ring but can't guarantee this will completely separate the 2 circuits due to the reading or do I give it a grade 3 ( needs further investigation) and issue a satisfactory pir? Help!! Cheers