Working in a 2 bed terrace and been asked to do a pir, the continuity on the downstairs ring final is confusing me and wondered if one of you chaps with a fresh pair of eyes could help me out. End to end continuity of Rn is open end to end of R2 is open but I'm getting a low fluctuating reading for R1. I've narrowed it down to 2 sockets which appear to be both the start and the other the end of the ring final and it's between these two sockets where I'm getting these readings. The wiring was done by professional type diyer fate a fire in the property a few years ago and the owner suspect not all the wires wire replaced. I could split the ring but can't guarantee this will completely separate the 2 circuits due to the reading or do I give it a grade 3 ( needs further investigation) and issue a satisfactory pir? Help!! Cheers:confused:
 
you could split the ring and have 2 radials, 16A MCB for each. this would comply and would not need a code at all.
 
if you split the ring that will go away. or, investigate further to trace and rectify the fault. you're the man on site, it's your call.
 
Are you sure it is a ring? If so then go round and check all the sockets for loose connections. If that doesn't fix it, then do the R1+RN check at every outlet, and R1+R2 at every outlet, this will help you find the break. And if all else fails you will have to split the circuit up and go wire to wire between outlets to find the problem. As you are doing a PIR, then i assume you are not there to fix it. I would personally give it a code 1 if you are sure it is a ring. you can't give it a satifactory because it isn't. Some remedial work is required, and overall condition, unsatisfactory.

As far as I am aware you can only give a satisfactory if it was done prior to 17th edition and everything is done to the regs current at the time of the installation, so you would only have code 4's doesnt meet BS7671:2008, and there are no "X" on the schedule of inspections.

Cheers........Howard
 
Last edited by a moderator:
if you narrowed it down to the two sockets remove the cable between them and change them to radials or run new cable between to reinstate the ring, running a temp cable between the two and retesting will prove if youre correct.
 
if you narrowed it down to the two sockets remove the cable between them and change them to radials or run new cable between to reinstate the ring, running a temp cable between the two and retesting will prove if youre correct.
i second that dont just put on 2 radials as its a ring for a reason ! either fix it or code 1 it - my 1st question to the customer will be ...
have you had any work done in the last few years electrical or not and start there !
 

Reply to Broken ring final? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
802
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
834

Similar threads

  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K
  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
853

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top