hello
tested a ring final circuit today a one of the socket outlets . (continuity of conductors)
r2 .85 ish (from memory)
rn .62 ish
r1 open circuit

turned the breaker back on and found 230 both ends of the broken ring?

turn off and took the ring apart some more including at the board
re assembled and r1 at the original socket tested = .63

how can it be live both ends of the "broken ring"??

confused :):)
 
There's somthing your not doing right in your testing and verification,
If need be your going to have to start at the cu and work your way round- happy hunting
 
Check the neutral as well. Presuming T&E your cpc should be in the region of 1.04 ohms given the resistance of the neutral. So perhaps there is a loose connection on the neutral?
 
if you have 230v on both cables then you should have continuity, only other thing i could possibly think of or suggest, is turn off all the other breakers in the board, except the supply to the ring and see if you still have 230v on both cables

if you do, then you have a big problem and should run very fast away from the premises screaming with your hands in the air!

performing evasive manouveres whilst carrying out the above action may help to accentuate the gravity of the situation... :)

Check the neutral as well. Presuming T&E your cpc should be in the region of 1.04 ohms given the resistance of the neutral. So perhaps there is a loose connection on the neutral?


could be parallel paths, i wouldn't probably focus on the ring continuity first myself
 
Last edited by a moderator:
could be parallel paths, i wouldn't probably focus on the ring continuity first myself

With the cpcs removed from the Earth bar to measure end-to-end resistance (r2) I can't see how there could be parallel paths.
 
If I am getting this correctly

You tested for continuity and had none on the lives at a socket
You tested for supply voltage on both ends at socket and had supply voltage
Tested elsewhere after putting it together and had ring continuity

For those tests to be accurate the problem has to be at that socket
A broken conductor at the socket that connects when the socket is closed perhaps
Otherwise I'm stumped
 
With the cpcs removed from the Earth bar to measure end-to-end resistance (r2) I can't see how there could be parallel paths.

quite simple really, think about it. he didn't describe the installation


also


confused as to why were you testing end to end continuity at a socket outlet? wouldn't you have performed this test at the board, then made your way around checking the continuity of 'the ring'

just curious
 

Reply to broken ring live both ends ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top