The oven i brought for my new flat is Bosch HBS534BS0B​


I have a cooker circuit thats on 40 amps fed in a think its 6mm not sure it might be 10mm is there any easy way to tell 6 and 10mm apart?

If the cirxuit is downgraded to 16 amps can that oven be wired into the cooker outlet point
 
the MCB is ther e toprotect the cable from MCB to cooker.if the cable is 6.0mm then a 32A MCB is fitted. if the cooker uses less, then as long as the MCB rating is above the actual current requirements, it complies
Iz>In>Ib.
 
the MCB is ther e toprotect the cable from MCB to cooker.if the cable is 6.0mm then a 32A MCB is fitted. if the cooker uses less, then as long as the MCB rating is above the actual current requirements, it complies
Iz>In>Ib.
Agreed, that is the main purpose of the MCB, but it's good practice to ensure it doesn't exceed the max. possible current by too much, just to reduce the size of the bang (technical term, also known as let through energy) if a short circuit occurs, if nothing else.
 
the MCB is ther e toprotect the cable from MCB to cooker.if the cable is 6.0mm then a 32A MCB is fitted. if the cooker uses less, then as long as the MCB rating is above the actual current requirements, it complies
Iz>In>Ib.
The oven 2.9kw which is 13amps so its 3 amps under the 16 amp breaker does it comply and as its not arrived yet I cant see the specs for installation
 

Reply to Brought a new oven in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
438
  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
697

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top