Hi Chaps
I am about to install an 8.5 Kw electric shower and a 2Kw water heater in a small flat that has a 60A 1361 main suppliers fuse.

The flat has 1*32A ring with 3 sockets, 1*20A radial with 5 sockets and 1*6A lighting circuit with 7 points.
If I allow 2amps for the lighting (at 66%), 40amps for the sockets (100% for the 32A ring and 8amps for the radial at 40%), then 37A for the 8.5Kw shower and 3.2amps for the 2Kw demand triggered water heater (at 40% of 8amps),
I get a total demand of 82 amps.

Am I reading the Time Current Chart correctly?
It seems to flatten out at about 3700 seconds at about 110 amps for a 60amp 1361.
Does this actually mean that it can carry 110 amps for 58 minutes?
Does it mean that it can carry my 82 amp estimate indefinitely?

Is my 82 amp estimate actually reasonable in the real world?
I cannot imagine that 8 sockets and 7 lightbulbs would really pull 42 amps?

Any advice is much appreciated.

CH
 
Last edited by a moderator:
Quit worrying, you'll not see anything like your calculated loadings. Those diversity formulas (excluding cooker formula) are so way over the top, it's almost a joke!! You'll be very lucky to see 40A for the whole flat!! And that's being generous too!! ...lol!!
 
awnsered your own question, turn everything on and clamp meter the live , youl see not up there... some say just take highest breaker and multibly the rest by 0.4

so.. 32+20+6+8 x 0.4 =26A add 37 for shower=63A your shower wont use full current unless youve skin like an elephant... i just know this as a rule of thumb from other posts on thbis forum
 
ther is no hard and fast rule for caculating diversity, and often your own knowledge of the installation in question will give more accurate figures than any calculation. Ive never seen a ring final in a house pull 32A. the 8.5kw shower will only pull 37A a) if your voltage is at exactly 230, and b) if it is working at full power. In reality,you wont have it anywhere near full power, and you wont have it on for long, so its very unlikely to cause an overcurrent device to pop anyway
 
my 8.5kw shower is on 30 A fuse, and never tripped ever in two years
so, 2 years between showers? worse than me. i have one every xmas, whether i need one or not.
 
awnsered your own question, turn everything on and clamp meter the live , youl see not up there... some say just take highest breaker and multibly the rest by 0.4

so.. 32+20+6+8 x 0.4 =26A add 37 for shower=63A your shower wont use full current unless youve skin like an elephant... i just know this as a rule of thumb from other posts on thbis forum

Just spotted this thread, because it is similar to a question I have come up against, practicallities v regulations, what figures should Colonel Haiti use for design purposes and the regs?

Furthermore, and similar to my problem, if you take a similar DB with the new shower as defined by Colonel Hathi and put it 40m away from the incoming supply, and you have to join them with 3 core SWA cable buried in the ground, what size SWA should you use? Calculating the Max Demand using OSG gives the figure Colonel Haiti came up with, so do you use a SWA big enough for the calculated demand or one big enough from experience and which is the correct way by the regs?
 

Reply to BS 1361 Time Current Characteristics in the Australia area at ElectriciansForums.net

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top