Cornwall
Hi guys,
Just testing a small campsite.
It is fed via a swa tns. OCPD is a 60a 1361 in a sw fuse.
Does anyone know why 1361's are not in bs 7671??
Or am I being thick? Lol.
The BGB (2011) changes included the fuse standard change from BS1361 to BS88-3, and the curves are slightly different.
Max Zs values are still in the red OSG I think, or you'll have to look in an earlier edition of BS7671.
BS1361 fuses were withdrawn 1/3/2010 and therefore are not in BS7671:2008+A1:2011, they have been replaced by BS88-3:2010 see pages 55-56 and 296. For BS1361 data refer to BS7671:2008 and/or OSG:2008+A1:2011
Reply to Bs 1361 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
If the plug works in most sockets but not one, then the socket has a problem. If the plug is out of spec as nasty fake one, or been bent by abuse...