BS 1363 socket for EV charger - what kind of RCD? | Page 3 | on ElectriciansForums

Discuss BS 1363 socket for EV charger - what kind of RCD? in the Electric Vehicles Advice Forum area at ElectriciansForums.net

I'm sure this one has been debated endlessly on here, but as far as I'm concerned, if it's metal and partly buried in the ground it's 'liable to introduce an earth potential' so needs main bonding.
https://electrical.------.org/media...tdoors-a-supply-to-a-detached-outbuilding.pdf
Already read it, but thanks anyway. I've actually done quite a few garages and sheds, just never a car charger (up until now). I'm sure someone reading this will find the link helpful though!
 
The manufacturer of the car will specify what type of RCD is required.
Usually its a A type for anything up to 32amp. With larger and 3 phase charging point usually require a B type RCD.

If you using a 13amp socket I'd protect it by a A type RCD the charging lead will have a inline RCD too.
 
Last edited:
You can charge a Tesla from a 13amp socket my friend has one but I believe it took him around 24 hours to fully charge the car

I installed a IP65 32amp interlocked socket for him with a Separate earth electrode.
The data sheet from Tesla specified a A type RCD.
 
Not all BS 1363-2 socket outlets are suitable for EV charging.
BS 7671 Sect 722:
722.55 Other equipment
722.55.101 Socket-outlets and connectors

722.55.201.1 Each a.c. charging point shall incorporate:
  1. (i) one socket-outlet complying with BS 1363-2 where the manufacturer approves its suitability for use, or...
BS 1363-2:2016
1 Scope
...
Additional requirements are included for socket-outlets suitable for electric vehicle charging.
...
 

Reply to BS 1363 socket for EV charger - what kind of RCD? in the Electric Vehicles Advice Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
947
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K
  • Question
You need a CT clamp at main tails, it depends on the rules where you are - you used to be allowed wireliss ones (such as MyEnergi Harvi), these...
Replies
14
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top