Hi all,

Do you know when BS 3871 Type 2 MCB's where not allowed to be fitted to a new circuit?

How should they be recorded on a EICR, as a BS 3871 Type 2 or BS 60898 Type B?

On the EICR they have been recorded as the latter.

Many thanks

B
 
BS3871 was superseded by EN60898 in 1991. You record BS3871 because that is the standard they were manufactured to not EN60898.
Type 2 and Type B have totally different tripping characteristics, the only similarity is that BS3871 Type 3 and EN60898 Type C have the same characteristics.
 
Thanks,

So if that circuit was installed in say 2008 then that breaker should not have been installed.

It should be recorded as BS3871 on the EICR as well then.

please correct me If I'm wrong.

Thanks

B
 
You record whatever breaker it is, you cant just use another breakers BS number.

I wouldn't be giving a code purely on the basis of it being a BS3871, even if it was installed after 1991.
 
Thanks for your replies.

I'm not a sparky, just a bit of a fed up landlord trying to sort out a rather poorly completed EICR and is being ignored by the contractor who expects payment in full for a report that I think is not worth anything.

I'm just trying to sort things out correctly. The EICR was for "All fixed wiring" with 1 three phase circuit in the agreed limitations, which was actually tested and data provided!

At the moment out of 3 DB's 1 Main and two sub mains there are 9 three phase circuits and 24 single phase circuits. On the EICR it shows 2 circuits with the correct circuitry and test data, 4 circuits have some data but is either incorrect or missing ie Incorrect Line or CPC csa, short circuit capacity, protective device type or rating. 1 has circuitry information but no test data and the last two have LIM in the circuit description.

I'm still working my way through the single phase stuff that's why I'm asking about the BS3871 on the EICR it has been put down as a EN60898 Type B just another thing on a even longer list and before anyone says anything the person was there for 3 days and had full access and it wasn't cheap!!

Thanks

B
 
If the contractor is part of a scheme, they should have a documented complaints procedure.
ask them for a copy of it,

put your complaint down in writing and email it to them, give a timeframe that you expect a response by.
 
James

They're NICEIC, I wrote to them once to tell them that the report was missing data and incorrect, I wrote to them again, recorded delivery with the first letter, and offered them to correct the EICR produce a new one or issue a credit note and gave them a time period to do so. I had a reply of please pay by a certain date and if you can't please phone and speak to the MD. My letters where all addressed to the MD and I made it clear the reason why I was withholding payment.

Thanks

B
 
Phone and speak to the MD and tell him straight. Tell him you want the Qualified Supervisor (as per certificate) on site to inspect and compare the paperwork with the installation.
If what you say is true, they haven't got a leg to stand on.
 
Last edited:

Reply to BS 3871 mcb on EICR in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

Had a quick look this morning as it’s local. It’s a full rcbo starbreaker installed in the kitchen pantry but unfortunately it’s plastic...
Replies
10
Views
2K
There is one reason to have an inspection every three years instead of the five. It’s more work and money for them 😁😁
Replies
15
Views
2K

Recommended Sponsor News

  • Article
thanks for the clarification. ( also thanks to Dan. ).
Replies
6
Views
2K
  • Article
More info on link below http://sbsc.uk.net/
    • Like
2
Replies
22
Views
9K
  • Article
Happy Friday Everyone! Subscribe for more jokes direct to your mailbox or send us your own jokes to be in with a chance of featuring, by clicking...
    • Like
2
Replies
27
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top