BS 3871 Time Current Characteristics ... again! | on ElectriciansForums

Discuss BS 3871 Time Current Characteristics ... again! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Joined
Jan 12, 2013
Messages
557
Reaction score
196
Location
Forres, Moray Coast, Scotland
Dear all, I recognise that this is a reprise of earlier queries ... and yes I have looked at the EIEMA document on the subject! I have just tested a modified lighting circuit protected by a venerable BS 3871 5 A MCB. On its side it is marked as follows, commas included as separators for clarity:


250 V, Max 5 A, M1 15/45 A M 1.5
TYPE TESTED TO BS 3871
MADE IN FRANCE RCT 40 °C


I am interpreting this to mean that it is a BS 3871 5 A type 1 MCB with a breaking capacity of 1.5 kA. Being one of the NKOTB ... I do not have either the max Z[SUB]s[/SUB] value for this or more importantly a copy of the time-current performance curves for this family of MCBs. I believe that the curves were last published in the 16th Edition of the BB; I am sorry, I didn't note which colour ...

In view of the fact that I also need to test and document a change to a 15 A radial socket circuit, and I like to do things and take responsibility for them myself, and there will be more work to do on this installation I am sure in the future, I would prefer a copy of the curves! Can any of the old(er) timers assist?


Yours Aye


GB
 
Last edited:
Max Zs 9.2 ohms based on 80% of the value given in the regs for a 5A type 1 MCB to BS3871

3.06 ohms as above for a 15A MCB

Type 1 curve is In X4
Type 2 " " X7
Type 3 " " X10
 
Last edited:
deleted. usually the figure aftere the letter M is the kA rating. not sure what the 15/45 followed by M 1.5 means.
 
so why put the kA rating of 15,20,30,45A MCBs on a 5A?

They could be anything from the manufacturers part/batch/model number those Tel, I was commenting on the M numbers, which as you say are the kA ratings, other than that your guess is as good as mine.
 
The lower M1 might be Ics
The higher M1.5 the Icu

Thanks to all who have contributed so far ... not quite what I was hoping for, but I have clearly added to the confusion by my transcription of the inscription! I will need to check the original next week and post an update. Having read the discussion, I think that it is likely that the ratings are 1 kA for the 5 A MCB and 1.5 kA for 15/45 A MCBs though as the question has arisen in other members' minds why would the ratings for 15 - 45 A MCBs be on the side of a 5 A. I will also pull a 15 A MCB to check the text and take photos of both!

As to Ics and Icu, I am no expert ... my expertise, indeed my life, does not reach back to the 60's though conception does just ... but, my reading of the EIEMA document suggests that this terminology was introduced by BS EN 60947-2.

Expert ... ex as in hasbeen ... spurt as in leak under pressure. Quote - Ex RN Submariner 2 1/2 'ring' supply officer!
 
Last edited:
Ics is the max fault current it can safely switch, and still be serviceable.

Icu or sometimes Icn is the max fault current it can safely break, but not be re-usable

I already gave you the trip curves earlier for the 0.1 -5 secs disconnection times
 
Last edited:
Max Zs 9.2 ohms based on 80% of the value given in the regs for a 5A type 1 MCB to BS3871

3.06 ohms as above for a 15A MCB

Type 1 curve is In X4
Type 2 " " X7
Type 3 " " X10

... so is that 0.8 x 12 = 9.6 Ohms or 9.2 Ohms? Whichever way, with a Z[SUB]e[/SUB] or according to GN3 Z[SUB]db[/SUB] as this is a sub-main of 0.19 Ohms and an R1 + R2 of 0.39 Ohms, Z[SUB]s[/SUB] for the lighting circuit is well inside at 0.58 Ohms ... safe as houses! I won't be recommending a new board yet then!
 

Reply to BS 3871 Time Current Characteristics ... again! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
227
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
638

Similar threads

The contacts are pushed open by a cam as the shaft is turned so they operate quite slowly. That's fine on AC as any arc is self-extinguishing at...
Replies
2
Views
914

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top