View the thread, titled "BS 7288 British Standard that specifies residual current devices (RCDs) for socket outlets used in households and similar" which is posted in Electrician Courses : Electrical Quals on Electricians Forums.
Jock from the north
Supporter
Without looking in regs have rcd spur units found their way back in book .I've been going through test sheets all day but I'll look after my spag boll.
531.3.4.1 bs7288 only provide additional protection.
There was mention on the forum at the time that they crept back in in the 1st amendment after being missed out in the initial 18th Ed.
It might have even been in a corrigendum (spelling!)
Upvote 0
Yeh there def not in initial 18th but are in amm 2 with a note "only provides additional protection" and can be operated by ordinary persons
Upvote 0
Well…. What else would you want them to be doing anyway?? By virtue of them being a socket outlet, fault protection is by ADS and over current protection by OCPD already.
Upvote 0
These can also be FCU RCDs, which could be used to protect fixed wiring. For what ever reason, these can only be additional protection, and can't be used to meet disconnection times in the way that RCDs to BS61008 etc can be. (although the BS1362 fuse in it could be used to meet disconnection times).
Upvote 0
Yes, but again an FCURCD won't protect the cables supplying it. It depends what exactly is meant by the statement in BS 7288.
Upvote 0
Not sure I follow? You wouldn't normally install an RCD of any type and expect it to protect the supply cables, only those downstream.
No, you wouldn't. But my point is that it may be making it clear that those circuit conductors aren't protected, whereas with an RCCB or RCBO upstream they obviously are. Don't forget that not everyone thinks as logically as you do, so that may be where the statement has originated from. Just my opinion.
Upvote 0
What statement?is it a statement in bs7671 or on this thread
I was referring to a fcurcd at origin ie as close to a crappy Ashley rock board .I cant see why that wouldn't provide additional protection for say loft lights where ocpd met disconnection times .I would like to know what rockingit thinks.he /she assumes that fault and ocpd are met before bs7288.
Upvote 0
Indeed it can't, as an SRCD doesn't protect the supply wiring.
What???if the rcd spur is at the origin and clearly in the Regs as an acceptable method of rcd protection for additional protection why isn't it acceptable for say loft lights ,which to be honest the fcu is only usefull for lighting ,you wouldn't use it to provide additional protection for a ring main would you ??if you provided mechanical protection of 4 inches [I know i wish i was so lucky ]from existing consumer unit what is the issue.i don't think you think as logical as you believe.but maybe your far more intelligent than some persons ,not me give you credit for
Upvote 0
Reply to the thread, titled "BS 7288 British Standard that specifies residual current devices (RCDs) for socket outlets used in households and similar" which is posted in Electrician Courses : Electrical Quals on Electricians Forums.