Is a 100A BS 88-3 fuse suitable for being the service fuse in a TN-S system with a Ze reading of say 0.68.
Obviously a TN-S system will be quoted at 0.8, but I just worked out the maximum Zs on this 100A fuse to be 0.38?
Your thoughts...